Ok I will attempt to be a great deal more succinct in future posts.
I have often measured a small amount of leakage even of switch start fittings and this would be fine if consistent, the problem is the fittings are all breaking down, possibly due to the Tig welders. I have measured this hence I am aware they are failing, I also know which circuit (phase) is being affected. I have measured 65mA on half the circuit (four 6' twins)
The high frequency fittings are working without issue although I don't know if they will also succumb.
I don't think they have a huge batch of bad ballasts

A bit of the post has gone !

Apart form advanced age are there any other causes of premature failure on ballasts ? Could it be the Tig welders ? If so can the issue be rectified somehow ?
 
Query on the lights.... are energy saving lamps been used with a standard ballast designed for standard lamps as this can overheat the ballasts and give premature failure.
 
Query on the lights.... are energy saving lamps been used with a standard ballast designed for standard lamps as this can overheat the ballasts and give premature failure.

They are bog standard T5 fluorescent tubes darkwood in switch start fittings, (as supplied when installed) I am calling them ballasts but could they be switch start chokes ? anyway, what constitutes an energy saving lamp ? used within these fittings.
 