a small exercise for trainees. something to get the brains kicked in on a bank holiday weekend.

hypothetical scenario.....

i have a DB supplying a flat. max. demand is 60A. it is to be supplied from an external meter enclosed in an approved DNO cabinet. the distribution cable length is 30m and the Ze at the meter is 0.18ohms. PME earthing. The meter is a new one where the outgoing terminals can be isolated without breaking seals. The first 20m of the cable is external, with the second 10m clipped direct ( surface above false ceiling ) internally.

1. What type and size of cable?

2. What needs to be fitted in the meter box?

3. What essential tests need to be done ( apart from the final circuits, can be assumed that all have previously been tested OK).
 
Last edited:
Pfft I'm not doing your homework for you!

When you say external would that be buried? Will have a crack when I get home
 
external as in fixed to the brickwork on the outside of the building. no containment.
 
Okay Tel, I've had a look at this. Bearing in mind I've not done any real circuit design before, please go lightly on me - I'll await your advice with open ears.

1) I would say a 10mm SWA cable - but I'm not sure whether a 2 core or 3 core would be best. I've done the calculations and I think the armour of the SWA could be used as the earthing conductor - however, I'm not certain I've done these correctly and I'm not sure if there's any regulations that don't permit this. I've checked the calculations on the cable size and 10mm meets the CCC and also volt drop requirements. If using a dedicated core for earthing arrangements, it would give a Zdb at the load end of 0.25.

2) I'm really not sure on this, but I would say a 60a breaker in order to protect the cable in fault conditions. My reasoning behind this is the Cutout might have an 80 or 100a fuse which in an overload or fault might allow too much current to flow in the cable before the fuse can disconnect it. I'd also considered whether a time delayed RCD would be required, but I'm not sure it would be.

3) insulation resistance, R1+R2 (and R1+Rn), polarity, prospective fault current, and Zdb.


could be a million miles away with this, but very interested to see how I did being a complete n00b to this. Thanks
 
Okay Tel, I've had a look at this. Bearing in mind I've not done any real circuit design before, please go lightly on me - I'll await your advice with open ears.

1) I would say a 10mm SWA cable - but I'm not sure whether a 2 core or 3 core would be best. I've done the calculations and I think the armour of the SWA could be used as the earthing conductor - however, I'm not certain I've done these correctly and I'm not sure if there's any regulations that don't permit this. I've checked the calculations on the cable size and 10mm meets the CCC and also volt drop requirements. If using a dedicated core for earthing arrangements, it would give a Zdb at the load end of 0.25.

2) I'm really not sure on this, but I would say a 60a breaker in order to protect the cable in fault conditions. My reasoning behind this is the Cutout might have an 80 or 100a fuse which in an overload or fault might allow too much current to flow in the cable before the fuse can disconnect it. I'd also considered whether a time delayed RCD would be required, but I'm not sure it would be.

3) insulation resistance, R1+R2 (and R1+Rn), polarity, prospective fault current, and Zdb.


could be a million miles away with this, but very interested to see how I did being a complete n00b to this. Thanks

A 10mm2 SWA would not comply on Volt drop mate. Remember that there will be Lighting off that sub-main. 6.9volts is your max. I got 16mm2 as compliant.

It would be best to protect the SWA with a switch fuse so as to achieve discrimination with the MCB's. The DNO would require this also.

Is there any extraneous conductive parts in the flat?
 
Yeah tel pm'ed me about the switch fuse. I hadn't realised that about volt drop but just done a little research and of course it makes sense that the drop is from the origin to the final circuits.
 
1omm cable 4.4mV/A/m.

( 4.4 x 60 x 30 ) /1000 = 7.92V. so at max demand the VD would exceed 3% as you rightly say. however, in the real world, the likelyhood of the installation drawing the full 60A max. demand is rare. it was a ---- up between 10mm and 16mm and in the end 10mm was selected.
 
1omm cable 4.4mV/A/m.

( 4.4 x 60 x 30 ) /1000 = 7.92V. so at max demand the VD would exceed 3% as you rightly say. however, in the real world, the likelyhood of the installation drawing the full 60A max. demand is rare. it was a ---- up between 10mm and 16mm and in the end 10mm was selected.


The voltage will more realistically be nearer 250 than 230. It is where i live anyway. Obviously this fluctuates.
 
thought you were still on D.C. down there. :38:
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

telectrix

Mentor
Arms
-
Joined
Location
cheshire/staffordshire
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)
Business Name
Telectrix

Thread Information

Title
for trainees
Prefix
N/A
Forum
Electrical Course Trainees Only
Start date
Last reply date
Replies
8

Advert

Thread statistics

Created
telectrix,
Last reply from
telectrix,
Replies
8
Views
180

Advert

Back
Top