I hope I'm reading this wrong as I've read this as you having disconnected the neutral of a circuit and then switched the circuit on?
If I'd even suggested that as a testing procedure where I used to work I think I would have been putting my job in jeopardy!
 
I hope I'm reading this wrong as I've read this as you having disconnected the neutral of a circuit and then switched the circuit on?
If I'd even suggested that as a testing procedure where I used to work I think I would have been putting my job in jeopardy!

In an empty building with that being the only circuit energised, yes I did
 
In an empty building with that being the only circuit energised, yes I did

I can honestly say if you were working for me you'd be lucky to still have a job after doing that.

Maybe I'm being harsh, but it is one of those things which was drummed in to me as an apprentice, never energise a circuit with either the cpc or neutral (if it has one) disconnected!

The only time I've ever really lost my rag with an apprentice is when they did this.
 
I suspect you have a shared neutral somewhere on those circuits that's effectively connecting all the phases together when a load is switched on on the circuit, have disconnected all the neutrals from the neutral bar, have a load on L1 and L2, very low load on L3, have created an unbalanced delta system where L3 is acting as the neutral for L1 and L2.

Something along those lines anyway.
 
...........What are you trying to prove by even doing this? It's not even a test you should be doing!

I hope I'm reading this wrong as I've read this as you having disconnected the neutral of a circuit and then switched the circuit on?.......

I also didn't understand exactly what tests were being made and why.
Spurious and confusing tests are going to produce spurious and confusing readings I guess. Disconnected neutrals will float, their voltage with respect to other parts of the circuit will be fluid, just stick to the recognised testing regime in GN3. Floating neutrals on a live circuit are highly likely to damage equipment that's connected to the circuit, if you do this on the wrong circuit the damage could run into many thousands of pounds.
 
I also didn't understand exactly what tests were being made and why.
Spurious and confusing tests are going to produce spurious and confusing readings I guess. Disconnected neutrals will float, their voltage with respect to other parts of the circuit will be fluid, just stick to the recognised testing regime in GN3. Floating neutrals on a live circuit are highly likely to damage equipment that's connected to the circuit, if you do this on the wrong circuit the damage could run into many thousands of pounds.

Thank you for the constructive post
 