Fuseboard relocation....re-test required?

Provide a EIC. Should be the same as changing a mains board as you are effectivly disconnecting everything and reconnecting. Obviously number of points isnt going the change etc. For the sake of a cert, global IR and 8-10 R1+R2 tests to make sure your insurance is covered then i would just spend the extra hour.

Unless you did the original install, then just copy over onto a EIC.

If you didnt, you dont know if its been tested properly.
 
Last edited by a moderator:
I don’t think, not issuing a certificate is on the cards.
What is being asked, is whether basic I&T on the CU would be sufficient, or would a complete I&T of the whole installation be required.

The whole installation, changing or repositioning the consumer unit means doing a EIC
 
Correct spinlondon!!! Just need to know if I should test whole installation again? Can't see the point personally as I havn't actually touched the "installation", it is all still as it was 1 month ago when EIC issued. Only change on cert would be "location of Consumer Unit".
 
The difference in quote costs isn't an issue, as I know i've pretty much got the job(if I want it), but i'm just after a realistic answer as to weather or not i NEED to test the whole installation as the customer wants a very detailed quote eg. work involved and exact costs.
I have spoken to the original installer (who isn't interested in the alteration job) and he reckons it voids all his certs/insurance etc if I touch the CU......is this true?
 