It wasn't caused by the omission of a 3a fuse, because a current far exceeding 3a could flow for a long time on a seized fan motor, sufficient time to cause the motor to seriously overheat before the 3a fuse blew.I think I've posted on here before about a fire in a new build near me which the rumours said was caused by the omission of the 3A fusing required by the instructions.
It wasn't caused by the omission of a 3a fuse, because a current far exceeding 3a could flow for a long time on a seized fan motor, sufficient time to cause the motor to seriously overheat before the 3a fuse blew.
I recall the case and the manufacturer of the fan used the omission of the 3a fuse by the contractor as a get out of liability, despite the fact that a 3a fuse almost certainly would not have changed anything.