Hi Guys, i have been asked to do some work in a garage, the main house is pme the garage has its own earth rod, the supply cable is a 10mm swa which has the earth connected at the disboard end in the garage but not at the house consumer unit, Is this corre4ct it doesnt seem right to me how is the sub main cable protected? Any advice muchly appreciated.
 
dont see why they would run a earth cable/swa and not connect it and go to the trouble of earth rod :S
 
i would connect the earth , rod being in wont defect it right enough will give better earth
 
No it isnt, they have stripped it back and flown into the plastic consumer unit at both ends. So will i have to treat the garage as a tt system in the eyes of the niceic?

What have they got to do with it?

Treat is as a TT as in the eyes of BS7671!!
 
Ridiculous, the pme reading would have been be under 0.50 I bet, but instead they ignore that and whack a pin in the ground giving a 30-100 ohm reading I suspect, lol, happy days
 
Ridiculous, the pme reading would have been be under 0.50 I bet, but instead they ignore that and whack a pin in the ground giving a 30-100 ohm reading I suspect, lol, happy days


Thats what i dont understand lol! Are you allowed to bring the earth out of the equipotential zone? Is this the reason perhaps?
 
looks like i was right you cant take the earth out of the equipotetial zone.

[h=2]TN-C-S (PME) Installations[/h]Where the supply company will not permit the export of the means of earthing to the supplied premises outside of those premises then special precautions will need to be taken for SWAs supplying remote buildings or equipment outside the supplied premises.
The reason for this restriction is to prevent the danger of exposed conductive parts and extraneous conductive parts connected to the installation outside the main equipotential zone becoming live in the event of the loss of the neutral under fault conditions. Also with long cable runs their will be a potential difference between the supplied earth from the neutral terminal and the general mass of earth.
In these circumstances it is preferred to connect the steel armouring of the SWA to earth at the main supplied premises and insulate the armouring at the remote end of the cable. This allows the SWA cable to be protected by the circuit protection device that is protecting the live conductor(s) of the cable. At the remote building the SWA is not glanded in a metal gland. The cable end can be terminated in a plastic stuffing gland or alternatively taken in to a plastic box or enclosure and the SWA cut back or insulated inside the box so that it cannot be touched. The cable is terminated in a plastic box and only the live conductors are then connected to the remote installation. No part of the remote installation must be connected to the SWA. The remote installation is converted to a TT system with a suitably selected RCD main switch and the provision of an earth electrode.
It may also be possible with the consent of the supply company to extend the main equipotential zone to the remote building. This can be done by using the SWA armouring as a combined CPC and main bonding conductor. All extraneous metal work in the remote building is connected to a common terminal known as the Building Earth Marshalling Terminal (BEMT). The armouring must be sized to comply both with Regulations 544.1.1 and 543.1.1. In addition with a PME system there may be network circulating currents flowing normally in the protective conductors which may raise the temperature of the SWA cable. In these circumstances the cable will need to be de-rated to accommodate this temperature rise. An alternative may be to run a parallel PVC green/yellow conductor of suitable size with the SWA. If this parallel CPC is buried then
it would need to be a minimum of 16mm2 to comply with Regulation 542.3.1 and Table
54.1 unless it is mechanically protected.

As an example a large building with a TN-C-S PME supply has correctly sized main protective bonding conductors with a CSA of 50mm2. An adjacent building is supplied from the main building with a 4 core 70mm2 XPLE SWA cable. The adjacent building
has service pipes and structural metalwork that are bonded to a BEMT. In this case the SWA armour would provide the means of earthing for the remote building and it would also have to act as a main protective bonding conductor. It can be seen from Table 2 above that the CSA of the SWA is 131mm2 which is adequate for earthing. However as this SWA steel is required to act as main protective bonding conductor connecting the BEMT to the MET in the main building it has to have a CSA equivalent of the 50mm2 copper main protective bonds in the main building.
The resistivity of copper at 200C is 17.2 x10-9. The resistivity of steel varies with carbon content from 100 to 1000 x 10-9. IEE GN8 suggests using a factor of 8 for the ratio of the resistivity of copper to steel.
So for the 70mm2 4 core cable in this case the steel armour has a copper equivalent of
131/8 = 16.38mm2. Therefore a supplementary copper main protective bonding conductor with a CSA of 50mm2 will need to be run in parallel with SWA feeding the remote building.

There is no maximum resistance for a main protective bonding conductor specified in BS7671 however IEE Guidance Note 3 states that the resistance between two bonded parts such as pipes should be in the order of 0.05Ω. Table 5 below has maximum lengths of bonding conductors that will achieve this recommendation.
If the remote building has an alternative means of earthing then the SWA armour or separate CPC would need to be rated to permit the maximum current flow likely to comply with Regulation 542.1.3.3.
 
nah, you import the tomatoes from greenhouse to kitchen. you don't need to know any more. that's womens' work. (tin hat on)
 
so we have armourings that arn`t tied to earth.....so that would be a start...wouldn`t it...lol....
might be good as well to confirm wether or not theres any extranious in there....
if not then its more a case of sortin out them armourings top end (i`m assumin its a 3 core SWA)?
the rod can stay as backup....
 
looks like i was right you cant take the earth out of the equipotential zone.

Read your post again, it is very much permissible to extend a PME equipotential zone!! Forget the statements made about the DNO, as they are rarely if ever interested....

Unless the out building is an excessive distance away from the main intake service cut-out/CU and has extraneous metalwork and/or pipework, you would be foolish not to take the superior earthing system with you. Even if it does have extraneous pipework etc, and is within a reasonable distance of the main property then a 3 core 10mm SWA or a separate 10mm run parallel with a 2 core SWA cable of any normal garage size cable will fulfill PME requirements....

From where or what publication did your cut and paste come from??
 