Been asked by a friend to put a socket and 2 lights into his garage this weekend (weather permitting!) and have come up with the following plan:

http://i.Upload the image directly to the thread.com/OcZTT.jpg

All using single core cables enclosed in 20mm PVC Conduit. The garage is fed by a 15m long run of 2.5mm2 SWA (already installed) protected by a 16A MCB on the CU.

As far as I understand the current regs it is accecptable to have a light running off a socket providing that it is protected by a 6a fuse (in this case in the form of an FCU, which also provides control). Can somebody please confirm this to be the case?

Will I require a way of isolating the socket from inside the garage and if so would a seperate FCU be accecptable?

Finally, do I need to get this work signed off by a certified electrician?

Thanks for any assistance given,

Andy
 
yes you an take lights off a socket using a FCU but the fuse will be a 3 amp why weather permitting doesnt the garage have a roof ??
 
Last edited by a moderator:
Does the house CU have RCD's? Any particular reason for selecting singles?

I was under the impression that if you are using PVC Conduit then singles need to be used? Would prefer using T&E as its cheaper.

yes you an take lights off a socket using a FCU but the fuse will be a 3 amp why weather permitting doesnt the garage have a roof ??

Just me being a wimp :P. Will make sure to use a 3A fuse tho, thanks.
 
You can use twin and earth in conduit do make sure the socket is RCD protected , and the work is classed as a minor works so would require a certificate
 
If you don't know the basics like if it is ok to use a FCU to feed a light from a socket or if you need an isolator for a socket should you really be doing this work?
 
I agree with Specialist, this is a new circuit so therefore is notifiable. The O.P shouldnot be doing the work as he asks "do I need to get this work signed off by a certified electrician?"
 
If the SWA is already installed, and the OP is just extending the existing circuit, there is no requirement to notify.
 