The pipe work passes continuity (R2 lead test) as the hob is earthed through the fused spur. This would still be classed as an extraneous conductive part, correct?
James,
As the guys have already stated................bonding the pipework and the gas bottle would be the perfect example of 'introducing' a hazard by unnecessary bonding.
An earth fault on the system would /probably raise said pipework and cylinder to mains voltage(think aluminium double glazing in past years) and the poor sod that comes to change the bottle will be it's path to earth.........probably