rattlehead85
Hold on... when carrying out alterations and additions you have to assess that the earthing and bonding is present and adequate for ongoing use. If the bond was installed to a previous edition and you have identified no safety issues how can you justify that it is mo longer safe. When you change the board you note on your certificate that the bonding has been verified for continuity and condition and that it is to previous regulations. Job done. Different kettle of fish if there us NO bonding or deterioration, then yes bonding to 17th would be needed.That's on a eicr. You haven't to comply with 17th if you change the fuse board