Sent to a property where there had been a small fire! They have had a new 17th CU fitted a lighting rewire and all Bonding brought up to Regs.
I get a call saying the plumber has gone to connect the gas meter to the incoming pipe and a spark was seen.
I test between MET and incoming gas pipe and show 10V. Ze is 0.23 and all seems OK. Thinking its just the gas fitter over reacting and thinking it just requires bonding so everything is the same potential, the little old dear shows me this.
After being shown the picture below I took a cable from the MET to the incoming gas and touching on the pipe there was a substantial spark almost like sticking a wire across a small car battery. I pulled the service fuse and still there was 10V and a big spark was created. At this point I was at a loss the fault was external and I passed it on to the Gas and DNO. Any Ideas?
For a spark like that theres obviously an issue somewhere,did you do a Ze by chance? just wondering if it could be a bad joint on the incomer,if that was the case and the cable fed more than one property then that could possibly cause what you are getting if it was a TNCS earthing arrangement.
...And then we can have the discussion about BS951 clamps on lead.
What exactly is the earthing configuration?
Op said Ze was 0.23
That's the old lead pipe, that caused the fire.. She walked past it when it was apparently flaming out like a blow torch. Loop at mains was 0.23. The sparking 10v was still there with service fuse out. TNS earthing...
Why pull the service fuse out? The main switch is a much better option for switching the installation off!
Because I can! And I also switched the main switch off I also disconnected the earth system just to make sure I wasn't missing something...............
It's not unexpected that a TNCS system neutral current wll partly divert down a bonded metallic service that is at earth potential, even on a healthy system. However in this instance I would be looking for a high resistance connection somewhere on the supply neutral,probably in the head,which would result in a substantial neutral current down bonding wires.
He reckons it's TNS
This is a post I made in 2010
This reminds me of a fault I had many years ago in my own house. I’d just installed gas central heating, the very last job for me to do was connect the gas pipe to the gas meter. Touched the two ends of the pipe and got a spark! Not good thought I, well to hell with it jammed the pipe together and soldered the joint. On putting a clamp meter round the pipe found 25A flowing through it :confused: Turned off supply to my house, still 25A, I’m getting confused at this point :confused::confused: I’m confused, the wife is frantic,:mad: no gas or electric now! Phoned electricity board, and after speaking to one of their engineers was told to keep both supplies turned off, they’ll get back to me. Not 2 mins later phone rings, we’ll be there in 20 mins! 4 vans and 2 overhead line wagons showed up! I did live in a rural area so supplies to the road were overhead. Much head scratching followed, at one point we disconnected the gas meter and slung that out in the back yard. In all seriousness this was the point the gas meter reader showed up:eek: It was decided to disconnect the entire road from the supply. By this time I’m not the flavour of the month with the entire road, we’ve now got 12 houses with out supply. The OH crew found a burnt line tap on the neutral. Further tests showed a neutral earth fault some where in one of the 12 houses. As I knew all the neighbours I got delegated to got to each house and isolate the supplies, how come this ended up as my job? Eventually there’s a shout from the OH crew as I isolated the furthest house on the road, “faults gone”. Electricity board senior engineer then goes in to “Hitler” mode, tells my neighbour “unsafe installation your supply will be disconnected until rectified”. While the OH crew are repairing the connections to the road I hijacked the apprentice that had come with the board and checked through the house. The apprentice found the neutral fault in a socket, the facia screw had bitten in to the core. OK now neighbours supply can be reconnected as well.
Now think about it the neutral for 12 houses was going through one 3.5mm screw. The house was bonded to the water pipe only. The current travelled along the water pipe until it got to my house, I’d just rewired and fitted CH. So it was a case of if it doesn’t move bond it, the current then went through my house and out through the gas pipe and nest. (I’ve never understood why a steel gas pipe is a better earth than lead water pipe, but it always is)? Just how in the name of god my neighbours house didn’t burn down I’ll never know. The fault must have been there for years.
Part of the reason for the electricity boards panic was there was a government fuel storage dump about 100m from the road. They use cathodic earth bonding which can cause fun and games. But had the fault been from there it would have been DC and not shown on my meter.
Thanks Tony, just for people's intrest, it's a 1920's mid terrace house with underground mains, the Earth strap to the sheath is a nice new braded type. And as for pulling the main service fuse, I was at a loss, so why not pull it? I may have missed something really stupid. But really this is one of the reasons I stoped posting here..
You post an interesting fault about a fire and sparking earth, and all someone's intreste in is that I pulled the service fuse... Really helpful in the question I was asking NOT!!!
I already said that and didnt get a flickin thanks!.....:mad2:....:wink:
sorry, I've had many N-E faults and loose N on PME systems.. Just lost me with a TNS system and supply to property off (OMG I pulled the fuse as well) and still got a low voltage but high current fault.. I'm still trying to picture Tony's explanation in my head, but I'm getting there...
Edd
Saw the same thing the other week. Loose bonding connection on gas was sparking, over how ever long it was doing it it melted through gas pipe and ignited gas. Dno came out and even with main fuse out it was still sparking. They were scratching their heads a lot. In the end they think it was a fault in another house but as this house had probably better bonding, the fault was coming down this bonding. Probably would never known if the connection hadn't been loose. No one hurt, but very lucky
Seen this sort of thing a couple of times on the DNO I worked for , the thing is there are so many new supplies installed of a TNS network and its usually a TNCS supply fed to new properties or even conversions in some instances , and then a lost neutral in one of the cable joints and then the bonding becomes live and transmits it through another place through the pipework external to the property , Ive seen it where the bonding wire had actually melted....
I am not criticising the act of pulling the service fuse, I have no issue with cutting seals and doing the same.
I am interested to know what logical thought process brought you to the conclusion that doing so was going to assist in this situation.
I cannot currently see the logic behind this and would like to learn from you what this is. It may be that there is something I do not yet understand which may help me in the future.
Is this not one of the reasons forums like this exist?
Edd, all you can do now as if I suspect the fault is external to the house is contact the DNO. Which I believe you have done.
If you can, be there when they attend.
The fault on my own house was a bloody good learning exercise for me as I was about a year out of my time. I’d almost no experience of domestic wiring systems. (40 years later I still haven’t got a great deal of experience for that matter.)
As for pulling the service fuse, I can’t see what the hell that has to do with this fault. The NWEB senior engineer that attended the above fault, his only comment was “you don’t believe in seals do you!” He became a good friend and helped me out with some of my projects later on.
Something to bear in mind, this fault won’t just be confined to the house in question.
My logical conclusion was I had tried everything else and the fault remained. I understand the problems with PME Systems and loose neutrals but had never seen it with a TNS System. When out of ideas try anything..... Oh and I'm techniquely allowed to pull the fuse as I used to sub to the EEB and have a nice little certificate...
There are many original TN-S supplies that are now serving both TN-S and TNC-S. Parts of the original cables lead sheathing having corroded away over time, or due to cable passing through aggressive sections of soil etc....
So it is more than feasible that one or more of this row of old terraced houses having a TNC-S supply, where a fault is being passed on to the gas/water supply services via main bonding cables. Something for the DNO to sort out, if you have proved to yourself that there is no fault originating from the property you are working in!!
Reply to gas pipe sparking!! in the UK Electrical Forum area at ElectriciansForums.net
Hi guys I am working in a warehouse where there is an inactive gas pipe and disconnected gas meter. The DB which has been upgraded now is on the...
Hi all, I am looking for some advice regarding old rewireable (3036) fuse boards in regards to additions and alterations. I am an electrician and...
4K
Hi guys I’ve seen people state in forums that it is permissible to bond a gas pipe as a continuation of the bonding of the rising water mains. Can...
5K
Those week I have mostly been fitting 20 x 10W flood lights on the sloping edge of a converted mill ceiling, nothing is straight, nothing level...
A 'Sunday challenge' for the qualified electricians.... Can anyone explain why a built-in gas meter housing box that is located 600mm above a...
6K