It is not something I would normally suggest trying out, but I appreciate your circumstances and the very real risk of not having heat at all.

Just remember to check things carefully and isolate the incoming power before doing ANY work on the panel, etc, as it might come back on at any time.

Hopefully we will hear back with some good news later!
 
It is not something I would normally suggest trying out, but I appreciate your circumstances and the very real risk of not having heat at all.

Just remember to check things carefully and isolate the incoming power before doing ANY work on the panel, etc, as it might come back on at any time.

Hopefully we will hear back with some good news later!
I completely understand that and appreciate your effort. I am definitely aware of the real dangers of both sending current upstream and handling live current. I will let you know how it goes
 
I do have one final question about getting a circuit in the box once I have an Interlock device. Our circuit box is full but has close to a dozen breakers for lights/switches. Can I switch several of those out for tandem breakers to make room for a generator breaker?
 

Attachments

  • 20210217_111517.jpg
    20210217_111517.jpg
    594.1 KB · Views: 47
I do have one final question about getting a circuit in the box once I have an Interlock device. Our circuit box is full but has close to a dozen breakers for lights/switches. Can I switch several of those out for tandem breakers to make room for a generator breaker?
For a permanent arrangement?

Usually you would get an transfer switch to allow you to move the whole panel from utility power to a local generator, but you will need to shut down a lot of circuits as your generator is probably only 30A or so and not going to run lots of high current stuff.

Also you need to check if your generator provides a 120-0-120 supply so you can run both 240V stuff and 120V stuff safely (though I think in the USA 240V stuff is usually quite high power and might be too much for your generator).
 
For a permanent arrangement?

Usually you would get an transfer switch to allow you to move the whole panel from utility power to a local generator, but you will need to shut down a lot of circuits as your generator is probably only 30A or so and not going to run lots of high current stuff.

Also you need to check if your generator provides a 120-0-120 supply so you can run both 240V stuff and 120V stuff safely (though I think in the USA 240V stuff is usually quite high power and might be too much for your generator).
Yeah, we can use an Interlock device to prevent backfeed but I'd turn all the other circuits off anyway. I was just thinking ahead for if/when I want to get it connected long term.

On the note of those breakers, is there any reason I can't convert some of those light switch ones to a tandem breaker?
 