The way I see it I can install the link at the genny and label it up accordingly. If it is ever sold then it can be removed, but the fact it is sold as a 'home or office' back up genny tells me that whereever it is used it is going to need a link in place anyway. The thing that worries me is, if that modified plug and cable gets into the wrong hands it could be lethal! People are more likely to consult an electrician if they come into possession of a genny labelled up as 'neutral earth link fitted, consult a qualified electrician before using' than if they come into possession of a seemingly normal but modified extension cable that may or may not have been labelled at some point in the past. I'm gonna have to contact the manufacturer next week regarding their warranty as I wouldn't feel comfortable doing it any other way.
It depends how the alternator windings are connected, sometimes it can be a pain converting a floating earth to a referenced earth. As this standby gen-set is going to be permanently located/positioned, it's no longer classed as a mobile/portable unit. As such it should be earth-neutral referenced....
I can't say how the windings are connected. Annoyingly the only picture I can find seems to be for a US version of the gen set:
I can't say how the windings are connected. Annoyingly the only picture I can find seems to be for a US version of the gen set................
This just highlights the actual problem of which the manufacturers are the single largest contributer. Firstly they mis-market their products, many of them are happy to call a site generator a back-up power solution. Secondly more often than not the design of the generator makes it impossible or very difficult to install it safely. Thirdly trying to find accurate information about the windings and general wiring configuration info you're invariably on a hiding to nowhere.
I'd suggest BY LAW manufacturers should be required to do as follows;
1. A schematic of the wiring of the windings and AVR and supply points on the genny should be on a sticker that's readily visible on the genny itself.
2. Every generator sold should be clearly marked with its intended use.
3. All generators should come with a termination block to allow easy the bonding of the N + E without dismantling the panels or electrical enclosure and without voiding any warranties.
4. Every generator should be sold with an earthing kit consisting of 3 x 2.4m copper earth spikes with couplings, wiring, clamps, spade and a sledgehammer etc.
5. A complete user manual and installation manual should be available for free from the place where the generator is sold. All information therein should be in English that's free from incorrect vocabulary and sentence construction.
Failure to comply with any of the above should result in the manufacturer, the importer and the wholesaler and their immediate families being arrested and prosecuted for attempted murder :)
Hello chaps
I understand some of this but not most of it, and it's not something I have ever been asked to do or would undertake - but I would like to understand it a bit more. Any helpful links?
Cheers
Hello chaps
Cheers
Get yourself a copy of Guidance Note 5 and immese yourself in sections 411, 413, 418.3, 551 and 717 of BS 7671 :)
What CR results do you get when you test the windings to the frame. I do mean CR not IR.
You’ve probably done this but I would be interested in the results.
Are you referring to a ductor test? If so, why would I need to carry this out? There is no connection whatsoever between winding and frame (on the piece of crap that the customer is now getting rid of).
Got it in writing from the manufacturer of the genny I have proposed to the customer. Fitting a link between the winding and the chassis does not invalidate the warranty :)
Did you manage to get a hold of the UK/EU version of the Genset wiring diagram. If nothing else, It'll be particularly useful for the customer and/or electricians in years to come, when it's out of it's warranty period!!