Discuss Ghost in the machine??? MCB tripping with no load? in the UK Electrical Forum area at ElectriciansForums.net
S
stonejenson
Client's cooker/hob stopped working - he called his service plan chaps and they said the cooker and hob were fine, but it was the supply, so he should call an electrician.
I went round and it seemed like an obvious problem, the quite old 45A isolator had had a meltdown and fallen apart inside - he said it had been hard to switch for sometime. I put it down to old age, as the 40A mcb had not tripped, so I swapped the switch - all seemed well.
2 days later, and it had 'popped' while in use, so I went back. New cooker switch was fine, but the supply CPC had somehow jumped out of it's connection, and I'm pretty good with getting my wires in tight, so thought it was odd, and why would that have caused the mcb to trip? (No RCD protection to circuit)
I took the oven out, it was fed from a socket via 13A plug, spur from the hob supply - I checked from consumer unit to switch, to cooker connection point - worst result was over 400Megs N to E.
I checked each appliance L-E and N-E, both fine. Impossible to test any L-N short out, as cooker has a clock, and hob is all touch controlled, so will have an internal circuit which will not give a good result anyway.
I reset mcb, zs result was fine.
I turned off, put it all back and it turned on ok.
I put it down to me possibly messing up the CPC wiring to begin with, and walked away a little confused, but pretty sure it was caused by the appliances themselves.
The next morning client calls and said it's tripped out again - AND NEITHER THE HOB OR COOKER WERE IN USE !?!?!?!?!
He's gone on holiday now for 10 days, so can't go back and check, but just thought about putting clamp meter over supply to see if there was any odd current draw when appliances were not on. I don't trust the hob's internal circuitry myself - but just wondered if anyone else had had a similar issue?
I wouldn't mind betting that the thermal ellement of MCB has been weakened/damaged by the original fault and now needs replacing. Going solely on your descriptions and accounts of this hook up, i can't see how anything else is being able to take out a 40A protective device...
Then again, you could possibly have a double fault one fault aggravating/affecting the other....
Just had a sort-of-similar one - domestic ring, MCB kept tripping out. Empty flat, between tenants, no loads and nothing even plugged in. Swapped the MCB, no different. Did a leg-by-leg isolation of the ring and found the dodgy section that was causing it - no continuity between the sockets either side, so I reckon a former socket plastered over, or a junction box buried in the wall/ceiling somewhere. Probably doesn't help your cooker conundrum, though....
pj
Reply to Ghost in the machine??? MCB tripping with no load? in the UK Electrical Forum area at ElectriciansForums.net
I’m going to call an electrician out on Monday, but curious if anyone has any ideas about this fault: I have a new kitchen fitted and two...
Hi all, we had our gas hob removed months ago and finally just got round to putting an induction hob in. Its a normal 4 ring induction but one of...
Calling all electrical professionals / boiler tradesmen -WE NEED YOUR HELP! Every so often (twice in the last two days) when running the hot...
So was on a call out today and cooker circuit kept tripping the RCD. Disconnected at the board and at the cooker switch and IR’d the cable and...
I have a 32amp MCB for my heating (heat pump) and when the heating comes on, it trips after a few seconds. If I push it back up it works fine...