No idea that's why I posted follow back and see, they hopefully go in ceiling void.
Probably not Ant, personally in my experience it's going to be a case of look and ye shall find, or transferring from flush to surface wiring systems, the first thing would be to find out how the RFC is wired, the right way or the wrong way makes a world of difference in any alterations.
 
Unless you can get back to a coupler try Demon Cato CL20GA Conlok Quick Fit Galvanised Steel Straight Solid Adaptor With Serrated Socket Grub Screw 20mm, can be fitted straight onto a cut end
Was going to suggest the same.
 
Tricky one that , what sort of test do you put on it once you’ve done the work , sure if you use containment for cpc you are supposed to use high current meter that injects 20/30a to check for good connections (Claire meter) if memory is correct , did a job for Ng Bailey for post office in early 90’s and we used containment as cpc
 
Tricky one that , what sort of test do you put on it once you’ve done the work , sure if you use containment for cpc you are supposed to use high current meter that injects 20/30a to check for good connections (Claire meter) if memory is correct , did a job for Ng Bailey for post office in early 90’s and we used containment as cpc
Clare B433R - Safety Testing - Seaward - http://www.seaward.co.uk/products/industrial-electrical-safety-testing-measurement-equipment/safety-testing/clare-b433r
Not sure if it was a post office spec on testing , but we defo had to use something similar to above
 
Good luck with that one.
I was asked to sort this out. They couldn't open the window to put the plant pots on their new 'mini veranda'.



upload_2017-10-10_19-35-14.png
 
I’d be certainly be asking for test results of any past tests if any , if not recommend full test just for peace of mind on an installation of that age
 
UPDATE:

Been back today ............ so I made the opening bigger into the wall:

Ari 2.jpg


And found that all the conduit was doing, was protecting the ring after it comes out of the cavity ....................

And one cable did link the 2 boxes together!

So all's good with the customer , who had agreed T&M for the work............. so I'll be sending an estimate later.


Thanks for the comments "team"
 