Gridswitch fuse spur?
M
Mike Blair
alright guys i have to get a 8 way grid switch but i have installed one. currently on a job where the electrician has left and i have taken over his job and has been a utter nightmare... there designer wants to use a 8 way grid switch 20amp double pole but someone was saying the fuses go in the back of the switch?!? never seen this i think hes confused! o_o
You can get fuse modules and/or flex outlet modules depending what exactly is needed. Of course they will take up a module each though in addition to the switch module!
You would have to specify your requirements more clearly.
Generally if you have a 20A DP switch then this is feeding a socket, for which the fuse will be in the plug so a fuse is not required at the switch.
If the 20A DP switch is not feeding a socket then is fusing down required, as the circuit should be protected at origin.
If you are switching four items then you can have both a switch and a fuse in the 8 gang grid.
I certainly would not recommend having fuses behind the switch plate as this is an inaccessible and inobvious nightmare.
could someone show me a grid with fuses and switchs i have never seen one tbh o.o thats why im confused as hell. and no one else on site "designer" etc knows -.-
instead of fuse spurs everywhere there using the grid switch so its all in one place
i see so i would probs have to get a 8way wago to split the feed into each fuse o.o haha
no, you loop the feed from 1 module to the next, then the next, etc.
No you feed to your fuse then from your fuse to the switch and then from the switch to the load. so in an 8way grid you could have 4 outgoing loads
For an 8 gang switch you could arrange things like this to provide witching and fusing for four items.
and wire like this
Personally I would feed the switch modules first and then the fuses. It means you aren't inserting or withdrawing a fuse into an energised carrier then if the switch is open.