Am I being really dumb and missing something?...the four heaters pull approximately 26 amps when on together? a C type breaker should handle this and in any case the load should not be touching the 32 mcb. Is it an RCD main switch, maybe there is a fault in one of the heaters? I'd be interested to find out what the answer is on this one.
 
I can't imagine anyone calling a RCD a main switch though, it may be a incommer in a dist board, or connected before a board but surely if it were a RCD then we would have been told by now, a pretty big thing to keep quiet in this case if so haha,

More likely a DP MCB.. lol!!
 
looks like it may be an RCD main switch, but I would have thought if the case it would have been mentioned and not just main switch tripped, very strange this one.
 
Ok We'll start again. The only time this new 'device' tripped is when I wasn't there after I changed the MCBs which were tripping two C types. There is an RCD on the dedicated board which hasn't tripped at any point. Fair point about the main switch thing but it's academic really because if it was an earth fault the other RCD should have tripped before any of the MCBs.
 
I tested the continuity and IR of the individual heaters and the whole circuit and I did Zs at the contactor. My clamp meter was out of batteries so I couldn't do a live current test.

IR was off the scale, Zs was normal as was continuity of the circuit. The only reading I thought was add was 4ohms resistance on the appliances.
 
OK off the scale=>500 Mohms, normal Zs means definately less than 1.44ohms as per p49 BS7671 Max Zs for Type B 32A bsen60898 MCB but in fact now that I have my test results with me 0.42ohms and batteries flat well I have no excuse for that one, seeing as how you're so keen to judge I'm sure you've never run out of batteries on a job.

However all that said, from your own 40 years of experience rather than criticising my terminology perhaps you could suggest a solution other than the one you've already suggested which I had already tried and which failed.:omg_smile:
 
OK off the scale=>500 Mohms, normal Zs means definately less than 1.44ohms as per p49 BS7671 Max Zs for Type B 32A bsen60898 MCB but in fact now that I have my test results with me 0.42ohms and batteries flat well I have no excuse for that one, seeing as how you're so keen to judge I'm sure you've never run out of batteries on a job.

However all that said, from your own 40 years of experience rather than criticising my terminology perhaps you could suggest a solution other than the one you've already suggested which I had already tried and which failed.:omg_smile:

Is it me or is this forum getting infested with people who can't take critisium??
 
Lol I'm ok with the criticism, what I'm after is a solution. I've had three pages of responses and only 1 suggestion that I haven't tried.

If heaters can't have high start up currents why are there companies that make products which control those currents?

If its not a high start up current why do they all turn on ok when they're already hot?

If I've got it wrong... well isn't that what this forum is for?

Oh and unlike some, I never charge if I don't fix it and I like to be sure which is why I on this site.

But the criticism is fine I'd just like to get this sorted so the people outside the pub can stop freezing their arses off.
 