Hi I have a question - just had an EICR carried out on property and the electrician has failed it giving C2 for "no supplementary bonding, or rcd on bathroom lights"

I've read through various posts here some of which suggest that could potentially be classified as just C3 and the EICR passed

Have attached the report here - if anyone could offer some help/advice on whether this work is really necessary
 
You have left the inspector's name still visible on the report.

The report is OK, there are some glaring common errors like ticks for successful operation of the rcd's you haven't got, c3 for omission of a label to test the rcd you still haven't got and so on.

If there isn't supplementary bonding in the bathroom, nor rcd then I would consider a C2 reasonable. I would more likely go C3 if the bonding was present.

It isn't a poor decision but borderline C2/C3 depending upon the circumstances and inspector.
 
What if it’s a pull cord and IP rated light fitting ? Is missing supp bonding really a c2 ?

I wouldn’t consider this a potentially dangerous situation
 
What if it’s a pull cord and IP rated light fitting ? Is missing supp bonding really a c2 ?

I wouldn’t consider this a potentially dangerous situation
True... but it doesn't say, I've only just read the report though, I'd actually be C2ing no RCD on the whole, as you've got downstairs sockets (well infact all sockets) that could reasonably be expected to be used outside with no rcd. No mention of a C3 for no rcd on lighting circuits in a domestic dwelling or for protection <50mm in wall either... (the last one Napit reccomend a C2 although i don't.
 
Sorry forgot to mention it has "downstairs" sockets but its split level flat - on 4th and 5th floor of building so definitely no sockets that could be used outside .

What is the "supplementary bonding" could someone describe to a newbie / novice at electrics? Would that require a full replacement of the consumer unit (as he has quoted for) ?

Thanks!
 
supplementary bonding is connecting all items in a location together with "earth" wire. this is to ensure that in the event of a fault, all metal parts are at the same potential. i.e. no voltage difference = no shock.
 
@telectix - thank you!

would that be within the consumer unit? ie would it requite a replacement unit for this .. or could the bonding be done to an old/existing unit?
 
would that be within the consumer unit? ie would it requite a replacement unit for this .. or could the bonding be done to an old/existing unit?
Supplementary bonding is not related to the consumer unit, it is typically earth cabling that you see connecting bathroom pipework (often in an adjacent immersion cupboard). But, if you have a modern consumer unit with RCD protection for relevant circuits, you can often omit this supplementary bonding, which is why sometimes you will sometimes see such an issue fixed by a new consumer unit.
 
thanks for the help guys !! appreciate it so much !! unfortunately can't send a photo of the consumer unit as I live in Singapore now (hence I rent out my flat) and not sure the tenants will know what/where it is. Think I might just have to eat it and pay for a new more modern consumer unit . He's charging £600 for this from quick google search that's not crazy / out of the ball park price?
 
Sorry, I wasn't aware that this is a property you rent out. In all honesty, we're two decades into the 22nd century, and it's time that all circuits in all domestic properties, rented or owner occupied, are RCD protected.
To avoid long distance hassle in the future, resulting from earth to neutral faults, I'd advise that you specify an all RCBO CU for the replacement, rather than an RCD split board.
 