Discuss Help/Advice with Long cable runs in garden in the UK Electrical Forum area at ElectriciansForums.net
Domestic property
Supply number 1
6 flood lights 4x400watt= 1600 watts
250meters from board to closets corner of tennis courts
Tennis court size
23m x 10m
My calculations are suggesting a
16mmsq cable
2.4% volt drop
Would anyone have any advice for doing long distances in a garden?
  • 10-16mm to a halfway point and distribute out for both circuits
  • apply diversity?
Supply number 2
Driveway 150meters
Cable length 200meters from fuseboard to 15 bollards lights (15x5w)=75watts
calculations
230v
75 load
1.5mmsq cable
Volt drop 0.8%
Many thanks
Domestic property
Supply number 1
Tennis court size
23m x 10m
16mmsq cable
2.4% volt drop
  • apply diversity?
Presumably all of the lights will be on at once if they are for a tennis court so there is no possible diversity to be applied.
I would take a 16mm submain, if that is the required size, to a suitable enclosure at the side of the tennis court. In the enclosure I'd fit a small DB to put each of the 6 floodlight positions on its own circuit.
Having each lighting position on a seperate circuit makes future maintainence and fault finding much easier.
How will this lighting be controlled?
Having a DB at the tennis court would also allow the installation of a socket relatively easily which will probably be quite useful at some point in time.
Thanks for reply, Yes to all floods on a same time- so your right no diversity.
I think I’m going to try 2x lutron RA2 selects or even a Quentic wifi module.
However this plan was for having the 2 cables back at the main house where the wifi would have been strong enough. But now looks like it may have to be a wise box near the tennis court.
You can still control it from the house by switching the feed to the tennis court if that is what is required.
Why the need for a wireless switching solution?
On p424 of bs7671 there is a correction calculation for operating temperature. Based on your load being nowehere near the max for the cable, it will lower your calculated volt drop, which should permit 10mm2 at 3%.
If you were prepared to allow a 5% drop, it might just about permit 6mm2.
Reply to Help/Advice with Long cable runs in garden in the UK Electrical Forum area at ElectriciansForums.net
Hi All, I’m after some advice. I’ll cut to the chase but I can give more detail if needed. A 400A sub main supply needs to be ran 100m, a pretty...
M
Hi all, very sorry to bother you with triv. I am in the process of sorting out some pretty shocking electics in a house that has been bodged at...
mbga9pgf
M