Help C&G 2357 Module 304

Discuss Help C&G 2357 Module 304 in the UK Electrical Forum area at ElectriciansForums.net

D

docomar750

Hi

Can anyone help as OLCI have informed me all tutors on leave. I am doing Module 304 and the question asked is: why does BS 7671 due to the PFC (1.2kA) not allow use of BS 3036 fuse in a domestic installation? Now i have looked trough the OSG and Regs but can see they do not stop the use of BS 3036 and although a S1A fuse will not work (1kA) a S2A fuse has a 2kA max as stated in the table. I know I am learning but the answer in the Regs does not seem to fit the question C&G are asking. Any advice would be greatly appreciated and accepted as said still learning and new to this.

Cheers
 
Hi,

From what I understand,

S1A--5A-10A (1kA )
S2A--15A--30A (2kA )
S4A-->30A (4kA )
Therefore you would be looking at your measured PFC and comparing this with the ratings of your Protective Devices,
You may want to look at Appendix 3 BGB ( Time/ Current Characteristics ), and also think about RFC with older cables <1.5 cpc and what this might do to your readings.
Others may have more knowledge on this.

Regards.
 

Reply to Help C&G 2357 Module 304 in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top