Mattp9394

Hi all, I have been a member for a while now and have been reading the forum with great interest but now i feel it is time to break my silence.

I installed three 400w low bay metal halide fittings today in a very old farm shed and only one fitting will ignite if connected. if i connect up two fittings and operate the switch then they just flicker for about 20 seconds and then go out. same happens when i connect up all three.


  • Henley blocks into existing tails to a small 5 way board fitted with a 100a main switch
  • metal 20mm conduit from board to the light switch position and the position of the lights
  • 2.5mm singles
  • 1 gang 1 way 10a light switch
  • 10A mcb
  • lights wired into kilks plugs that attach to the through boxes

i had to leave it with one fitting plugged in as it was getting late and i was running out of ideas, the mcb never tripped and i belled out all of my work and found no faults

any ideas would be very great full as i am really stuck here
 
Last edited by a moderator:
400V or 400 W ????
If you switch on a metal halide light it heats up very quickly. If you switch it off, it requires upto 10 mins to cool before it will strike again.
Dont panic (yet)
Check your lamps are tight into their holders. Some of the less expensive types have a poor base and the contact area in the base is small.
I've seen metal halide lamps flicker during heat up in lighthouses, its common enough, but once they heat up, they are fine.
 
yeah I meant 400w. I will try them again in the morning after they have defiantly cooled down. Could it be anything else for me to try tomorrow just in case?
 
Last edited by a moderator:
I take it all the control gear is contained within the fitting and come pre-wired and all is needed is for you to give it its supply ??
Only thing I can think of at this stage is check your wiring and connections. Only other thing I can think of is that they, Metal Halides, are sensitive to lower voltages, I've seen 1 or 2 refuse to strike due to low voltage issues. (Below 200V)

Good luck
P
 
which one strikes and stays on is it the closest one? as mentioned above check all voltages/connections at fittings. if your getting 230v l-e and 230v l-n then the issue must be with the fittings.
 
Just re-read the older posts.....400V lighting system???
Thought it was 400W:90:
Surely the supply voltage is 220V,,,while the lamp is striking you'll get upto 280V, but it soon settles back to 220 after heat up / striking..
Never come across 400V metal halides before......but the capacitors are rated at 400V.
 
Check the control gear recently had problems with poor terminations causing lamps to flicker but not strike. ballast cables terminated to heat resistant sheath rather than copper
 
Just re-read the older posts.....400V lighting system???
Thought it was 400W:90:
Surely the supply voltage is 220V,,,while the lamp is striking you'll get upto 280V, but it soon settles back to 220 after heat up / striking..
Never come across 400V metal halides before......but the capacitors are rated at 400V.

To cope with the peak voltage Phil
RMS*√2
 