That's a good point, didn't think off that. Will do, I will drill through as you say, Nice one! Cheers Derry0178.if you are feeding SWA through a wall, drill at an appropriate angle so that the SWA comes out of the wall without you having to make a tight bend. hope you can see what i mean. ( oh, and don't praise trev too much. he'll get big-headed. :44![]()
If you can ,Drill from outside in .You can make good the plaster on inside but a blown out brick on the out side will look messy.
How are you going to terminate The SWA into the CU ?
Think you'll find it didn't say use rcbo and RCD sockets in series at all, I said .......rcbo and bog standard sockets.Great point "not clever" but you can't rcbo the house and put a RCD socket in garage as its against regs, can't have 2 30ma RCDs in series, plus you won't need rcbo in house as its swa.
like you said RCD socket in garage but instead of FCU use the 1G RCD module instead to control the lights with a 5A fuse installed.
Derry is either newly qualified or almost there
You could use a 25mm metal conduit end box on the outside of the house (outlet facing down) make off the SWA into that with a water proof gland and then run the cable inner sleeving still on though the wall into the back of the CU you will have to run an earth lead to the conduit box though (USE 3 core swa)