I bought a Gainsborough shower engine from Ebay. I fitted it and it works well but the live(red) cable is heating up.
Have i wired this in incorrectly or is there a likely fault on the unit.

I am not an electrician and simply replaced an existing part.

I am concerned that I have wired the live and neutral the wrong way round

please advise

thank you ladies and gents
 
Peter,
You might want to get a sparks in to take a look.
Wire could be heating up due to loose connection, or the cross sectional area of the cable may be too small for the load.
ALthough connecting the L and N is incorrect for different reasons and needs to be addressed it wouldnt cause the heating u described on its own.
Needs addressing ASAP!
 
what's your location. sure there's a member close enough to you to come and have a look at a reasonable cost.
 
One or 2 members in your area. Try the electricians in your area forum.
 