Hi chaps,
Could someone advise on where point A and B on a bdr91 thermostat go to which terminals on a baxi 600 combi, does a go to terminal 1 and b to terminal 2 ? Or the other way round ? Also do i need to link L to A ? Thanks.

20181208_204143.jpg

20181208_204208.jpg
 
B1 and bk2 it doesn’t matter which way round. Conventionaly you would connect bk2 to A and b1 to B.


Thanks Lee, its currently wired A to b1 and bk2 to b, i will swap them round for peace of mind, as the boiler instructions say the 230v switched signal needs to go to terninal 1, i wasnt sure if a or b was the switch signal, do i need to put a link from L to A ? To make it 230v as such ?
 
No bk2 provides the 230V output and the A and B are just a normally open contact that closes when the thermostat tells it to and sends the live to b1.

Obviously you also have to power the receiver with a line and neutral.
 
No bk2 provides the 230V output and the A and B are just a normally open contact that closes when the thermostat tells it to and sends the live to b1.

Obviously you also have to power the receiver with a line and neutral.

Cheers, at the moment its got live and neutral to the reciver from fuse spur, the boiler also has live,neutral and earth from fused spur as it needs permant live i believe. Then had a wire from a in reciever to b1 on boiler and another wire from b in reciever to bk2 on boiler. That sound right ? Cheers.
 

Reply to Help wiring bdr91 to baxi 600 combi boiler in the Central Heating Systems area at ElectriciansForums.net

Similar Threads

Hi folks, I'd like to get my Nest thermostat up and running with the gas combi boiler (Worcester Greenstar HIghflow 440 Standalone). FYI - I...
Replies
9
Views
1K
At the moment it depends on the weather on how well the central heating works, the main problem is the Nest Gen 3 thermostat only measures the...
Replies
7
Views
681
I've always thought I was quite good a wiring heating systems, I can do Y plan, S plan, UFH set ups, "normal" thermal stores etc, you name it and...
Replies
4
Views
941
Hi, my wife and I have decided to bite the bullet re the costs of an electric combi boiler in an off-gas grid one bedroom flat where space is so...
Replies
10
Views
2K
Picture taken from another post as my phone is a potato. We have had a Potterton Promax Ultra 24 ErP Combi installed. I am looking to install a...
Replies
7
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock