Hi all this is first time on here so please take easy.

i am installing a built in double electric oven and about 2 meters away a 4 ring electric hob.

My problem is i only have one 6mm feed into the kitchen how would i go about wiring up the oven and the hob to that 1 cable.

I am unable to run another cable from main board as all been plastered etc.

any help would be great thanks
 
As long as the loading works out ok, just connect it to the isolator thats there for the hob
 
A few more facts needed whats the size of both the hob & double oven how far is the run to the CU and how is the cable installed etc?
 
the cable is current coiled up at ceiling level

can i feed a cooker outlet with it and then run another cable from that outlet around kitchen to a fused spur and the from the fused spur to a second outlet ready ti wire the hob in both outlets would be 45amp.
 
take your 6mm to an isolator. from there run to a double outlet, one for oven, one for hob. as long as the cable is protected according to the CCC calculated according to the ref. method of installation, fine.
 
the cable is current coiled up at ceiling level

can i feed a cooker outlet with it and then run another cable from that outlet around kitchen to a fused spur and the from the fused spur to a second outlet ready ti wire the hob in both outlets would be 45amp.
What power do they each draw?
 
Have a look what Tel has posted that would be the way to do it.

When you do the maths re diversity you will be looking at 21A or 26A depending if you have a socket outlet on the cooker switch!
 
His brain will go in to
PBGoldsrelay.jpg
 
as said before, with diversity applied your total current demand is < 30A so 6mm cable on a 32A MCB will be adequate for both appliances.
 