Hi
I have a apex domestic vo. The light is on red. What does that mean? The switches on the product are red and grey. The red switches are up( i believe in on position) however the grey swith is down( i believe off) is that how they should be. Can someone please help
 

Attachments

  • 15807147025726402306993658528760.jpg
    15807147025726402306993658528760.jpg
    68.4 KB · Views: 31
The grey switch on the far left is in the off position as shown by the green flag in the little window. Push it up to turn on. I strongly suspect the VO is part of your PV system to regulate the voltage to your home.

More pictures to show the installation would be helpful to confirm.
 
The grey switch on the far left is in the off position as shown by the green flag in the little window. Push it up to turn on. I strongly suspect the VO is part of your PV system to regulate the voltage to your home.

More pictures to show the installation would be helpful to confirm.
When i turn the grey swith up the small flag goes red????? Should the flag be red or green???
 
the grey switch unit is a MCB, 63A.the double pole switch on the right is an isolator. it's the type of device that would power a sub-main.
[automerge]1580720469[/automerge]
When i turn the grey swith up the small flag goes red????? Should the flag be red or green???
with the left switchup, it;s on and whatever it feeds will then have power. we need more info as it could be off due to a fault. switching on blindly could cause problems.
 
the grey switch unit is a MCB, 63A.the double pole switch on the right is an isolator. it's the type of device that would power a sub-main.
[automerge]1580720469[/automerge]

with the left switchup, it;s on and whatever it feeds will then have power. we need more info as it could be off due to a fault. switching on blindly could cause problems.
What info would tou like?
 
for a start, what does it feed? what is not currently working?
I dont know. I dont even know if the solar panel system is working. This is all I have. The grey button on the VO was down and flag was green. Now I pushed it up and its gone red
 

Attachments

  • 15807228368933902055619509901299.jpg
    15807228368933902055619509901299.jpg
    149.3 KB · Views: 26
  • 15807228943896775424519648393031.jpg
    15807228943896775424519648393031.jpg
    98.9 KB · Views: 23
  • 15807229242594334366657450081251.jpg
    15807229242594334366657450081251.jpg
    86.9 KB · Views: 20
not seen anything like that unit before (pic #1).. perhaps another member will recognise it.
 
think the blue box is your solar inverter. suggest you find a local sparks who is conversant with solar installations.
 
It looks to me like the VO has been wired in incorrectly. Please take another photo which shows were the cables from the meter go - do they go into the VO at the bottom?

Your PV ac arrives along the black cable into the small enclosure with the gray switch. There should be two cables from this enclosure which join with the two cables from the meter and then go into the VO input. The VO output then goes to the Consumer Unit.

In your current arrangement the solar is connected to the output of the VO when it should be connected at the input of the VO together with the mains from the meter.

The VO should be wired in as shown in Figure 2 on page 8 of 16 of:

https://www.waxmanenergy.co.uk/media/upload/eav00401_pdf02.pdf

You will need to call back an electrician who can rewire as in Figure 2. This is not job for DIY!
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Birmingham
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
DIY or Homeowner (Perhaps seeking pro advice, or an electrician)

Thread Information

Title
Help with domestic VO
Prefix
N/A
Forum
Domestic Electrician Forum
Start date
Last reply date
Replies
18
Unsolved
--

Thread Tags

Advert

Thread statistics

Created
Kamran,
Last reply from
marconi,
Replies
18
Views
2,814

Advert

Back
Top