Just be careful then, as some boilers use a Low voltage switching system for the thermostat. 0V to 24v so if you stick 239/240v up it you may blow up the PCB. Which isn't cheap to replace.
It's worked fine since installation, I used the boiler instruction manual to do this which is why I recommended that the OP also checks the manual
 
Yes luckily I found the Old manual and I did speak to the company who made the old controller to see if terminal 2 was 240-volt and they said with the bridge it would be so I know no it won't damage the motherboard
 
I probably should have been clearer, I've got a different boiler and it has more connections I just assumed most boilers would be the same in terms of the thermostat connection

No they are not all the same, and you shouldn't make assumptions when advising someone on how to connect something.
 