High Ze causing headache !

Discuss High Ze causing headache ! in the UK Electrical Forum area at ElectriciansForums.net

sythai

-
Arms
Reaction score
356
Hi Guys

Any advice/ pointers would be appreciated 😉

Have ‘pretty big’ new build house we’re wiring from scratch.

New supply in from DNO is PME, but we have Ze of 0.51 😕

Are DNO obliged to keep this under 0.35?

Wouldn’t be that much of an issue normally if regular size house and meter was attached to house.

Before we came along on the scene Client had separate garage block built, meter permanently sited in here.

We’ve run a SWA sub-main across to house DB 25metres away, but struggling on suitable overcurrent protection. Even at 80amps BS 88…. Max EFLI 0.40!

Don’t really want to be putting new build on TT system, if it comes to it.

Thank you
Sy
 
If you meet ADS by OCPD then you meet thermal constraints. If you meetr ADS by relying on an RCD then you may well not meet thermal constraints for L-N by the OCPD which is still covering that.
Correct, which is why I said earlier on that all aspects of the regs still need to be adhered to.

I grant you that some people may not check various aspects of the regs, usually because "it's always been OK in the past" but I think that happens all the time, I come across so much work where the person installing hasn't thought about it one bit - basically it's never designed, just installed.
 
Correct, which is why I said earlier on that all aspects of the regs still need to be adhered to.

I grant you that some people may not check various aspects of the regs, usually because "it's always been OK in the past" but I think that happens all the time, I come across so much work where the person installing hasn't thought about it one bit - basically it's never designed, just installed.

Incorrect. You only stated that after I had mentioned it. It often gets missed.

Applying RCD to a circuit to cover ADS goes hand in hand with checking Line-Line or Line-Neutral thermal constraints.
 
Not always. With MCBs, the let through energy tends to increase with increasing fault current. So the most onerous part of the circuit for thermal constraint is close to the origin, where ADS is assured

Generally it does work out with MCB's if you are operating with pfc's withing the breaking capacity of the device. At least it always has in the real world scenarios I have applied it. There is also the other variable of manufacturers data where you can go with faster times than the 0.1s in the regs which I believe has additional considerations attached that I can't remember what they are?
 
Generally it does work out with MCB's if you are operating with pfc's withing the breaking capacity of the device. At least it always has in the real world scenarios I have applied it. There is also the other variable of manufacturers data where you can go with faster times than the 0.1s in the regs which I believe has additional considerations attached that I can't remember what they are?
I don't think there any additional considerations for using manufacturer's data, it just replaces the I2t in the equation AFAIK.

Using, for example, data for a 32A Hager B curve, and using a 1mm2 CPC, it is possible to fall foul for fault currents of ~3kA or greater, and for higher fault currents for lower rated MCBs. So potentially a problem for old ring finals wired with 1mm CPCs, or other such circuits.

Interesting to note that the adiabatic equation only seems concerned with protective conductors, as far as the regs are concerned, as far as I can tell anyway
 
I don't think there any additional considerations for using manufacturer's data, it just replaces the I2t in the equation AFAIK.

Using, for example, data for a 32A Hager B curve, and using a 1mm2 CPC, it is possible to fall foul for fault currents of ~3kA or greater, and for higher fault currents for lower rated MCBs. So potentially a problem for old ring finals wired with 1mm CPCs, or other such circuits.

Interesting to note that the adiabatic equation only seems concerned with protective conductors, as far as the regs are concerned, as far as I can tell anyway
I think the adiabatic appears only to be related to protective conductors in the regs as it's included in that section and the CPC is usually the smallest (or at least the same size).

It is interesting that it is assumed to be limited to disconnection times of less than 5s but essentially the same equation is used by most cable design books for up to 30 secs.

(And they have different k values as the temperature change is included within the calculation rather than within the k value - so you get exactly the same result)
 
Yes, time delayed rcd on distribution circuits, standard rcd on final circuits - rcds as fault protection.

No need to convert to TT

leave it as TN-C-S and you can still use 0.4s / 5s but add rcd as fault protection where required.

So if the cable from the meter location to cu fails to operate in 5s due to fault, add a time delayed rcd.

If any final circuit fails to operate in 0.4s due to fault add a standard rcd.

If a circuit will operate within these times, then a rcd is not required for fault protection, but may be required for additional protection.
Thanks Julie
 
I don't think there any additional considerations for using manufacturer's data, it just replaces the I2t in the equation AFAIK.

Using, for example, data for a 32A Hager B curve, and using a 1mm2 CPC, it is possible to fall foul for fault currents of ~3kA or greater, and for higher fault currents for lower rated MCBs. So potentially a problem for old ring finals wired with 1mm CPCs, or other such circuits.

Interesting to note that the adiabatic equation only seems concerned with protective conductors, as far as the regs are concerned, as far as I can tell anyway
It was on the IET forum about why we should not use adiabatic for fault currents operating devices <0.1S or >5S. I couldn't remember but just found it again on there.

Going over 5S was more straightforward. Because the adiabatic is simplified it does not allow for heat loss, this results in artificially high csa's

Going under 0.1s was more complex. 0.1S is 5 cycles of the supply waveform and going below that could give rise to greater currents than calculated due to the waveform being asymmetric and becoming distorted.
 
Interesting to note that the adiabatic equation only seems concerned with protective conductors, as far as the regs are concerned, as far as I can tell anyway

I think the adiabatic appears only to be related to protective conductors in the regs as it's included in that section and the CPC is usually the smallest (or at least the same size).
My bad, it isn't only concerned with protective conductors:

434.5.2
A fault occurring at any point in a circuit shall be interrupted within a time such that the fault current does not cause the permitted limiting temperature of any conductor or cable to be exceeded.
 
Just to check Julie.... how does this work on my EIC please?
My recorded Zs reading for the BS88 will be higher then the max Zs reading of 0.40
Thanks Simon
Fill it in with the correct values, but in notes/remarks add something like "ads achieved via rcd as fault protection " - according to each circuit that needs it, for example lighting circuits probably achieve ads with the mcb so don't need it.

Then in 3.1 the last line rcd as fault protection should be ticked (and ideally the appropriate circuit number added - so rfc downstairs, shower... whatever).

You would still need to tick rcd as additional protection as a house requires it for lighting, sockets etc anyhow
 
Fill it in with the correct values, but in notes/remarks add something like "ads achieved via rcd as fault protection " - according to each circuit that needs it, for example lighting circuits probably achieve ads with the mcb so don't need it.

Then in 3.1 the last line rcd as fault protection should be ticked (and ideally the appropriate circuit number added - so rfc downstairs, shower... whatever).

You would still need to tick rcd as additional protection as a house requires it for lighting, sockets etc anyhow
Brilliant thanks - got it now, always learning 🙏
 
Fill it in with the correct values, but in notes/remarks add something like "ads achieved via rcd as fault protection " - according to each circuit that needs it, for example lighting circuits probably achieve ads with the mcb so don't need it.

Then in 3.1 the last line rcd as fault protection should be ticked (and ideally the appropriate circuit number added - so rfc downstairs, shower... whatever).

You would still need to tick rcd as additional protection as a house requires it for lighting, sockets etc anyhow
I don't know if you use particular software, but you may have to jump through a couple of hoops if the software blocks or alerts in the case where Zsmax is exceeded - but that would depend on the software itself.
 
I don't know if you use particular software, but you may have to jump through a couple of hoops if the software blocks or alerts in the case where Zsmax is exceeded - but that would depend on the software itself.
Use Easycert... but sure there is a work around.
Failing have used the Niceic ones direct on their website before
 
My bad, it isn't only concerned with protective conductors:

434.5.2
A fault occurring at any point in a circuit shall be interrupted within a time such that the fault current does not cause the permitted limiting temperature of any conductor or cable to be exceeded.
Nice one, that's the reg and the one that often gets fell foul of.
 
Even changing to TT, I assume at
Fill it in with the correct values, but in notes/remarks add something like "ads achieved via rcd as fault protection " - according to each circuit that needs it, for example lighting circuits probably achieve ads with the mcb so don't need it.

Then in 3.1 the last line rcd as fault protection should be ticked (and ideally the appropriate circuit number added - so rfc downstairs, shower... whatever).

You would still need to tick rcd as additional protection as a house requires it for lighting, sockets etc anyhow
I wouldn't add a note, BS7671 accepts an rcd can be used for fault protection.
 
No chance of using a BS88-2 63A fuse? I've have access to three different MFT, never got a matching Ze reading from any combination of them. One (Fluke) is always higher than the other two (Megger) with it not unusual to see a difference of up to 0.2 between the Meggers and the Fluke.

Be interested to see what the Zs is when the installation is completed as apposed to the Ze.
 
I've have access to three different MFT, never got a matching Ze reading from any combination of them. One (Fluke) is always higher than the other two (Megger) with it not unusual to see a difference of up to 0.2 between the Meggers and the Fluke.
I am going to try our other ones... we've got couple of other Meggers - be interesting to see
 
It was on the IET forum about why we should not use adiabatic for fault currents operating devices <0.1S or >5S. I couldn't remember but just found it again on there.

Going over 5S was more straightforward. Because the adiabatic is simplified it does not allow for heat loss, this results in artificially high csa's
The 5s is somewhat arbitrary and related to the ADS regs. In reality the issue is as you say, the CSA becomes larger than necessary as it is not accounting for heat loss (i.e. it is not really adiabatic). So it is a safe option, but a sanity check is if the computed CSA is larger than the necessary line conductor to match the CCC limit of the OCPD then you really have gone beyond the limit!
Going under 0.1s was more complex. 0.1S is 5 cycles of the supply waveform and going below that could give rise to greater currents than calculated due to the waveform being asymmetric and becoming distorted.
Sort of. What you see in the time/current plots is typically known as "virtual time" and it is the equivalent time at that PFC leading to the same I2t let-through. In reality, and especially for fuses that are quite energy-limiting, the time on the plot can be uses with tolerable accuracy even allowing for varying phase angle of the fault.

So while you might see an extraordinary short time like 10-100us listed at high PFCs, in reality the fuse arcs for longer but is limiting the current so you don't see anything like the PFC flowing. That is also seen on the plots of peak fault current where it is much lower than you get from MCB/MCCB.
 
I know a lot of people feel designing a circuit on a TN system and relying on a rcd for fault protection is a bad design but this is twaddle and this thread is a good example, a high Ze but even so it is still acceptable.
I would normally avoid relying on RCD if reasonably possible, but as you say where the only sane technical solution is RCD then it is perfectly good.

Same for the earlier comment about going TT, it is much better in most cases to have the low TN supply Ze used, even if it is not quite low enough for the sub-main, as it means the final circuits are likely to disconnect on OCPD alone which is a small extra reliability gain, as well as having lower touch potential during any fault.
 
New supply in from DNO is PME, but we have Ze of 0.51

We’ve run a SWA sub-main across to house DB 25metres away, but struggling on suitable overcurrent protection. Even at 80amps BS 88…. Max EFLI 0.40!

Actually there is something more fundamentally wrong here. If it is TN-C-S then, unless there is something very bad at the cut out, the supply Ze is the same as the supply impedance. With 0.51 ohms and 80A you would be seeing 40.5V drop in the incoming supply! That is more than the ESQCR limits of +10% -6% on 230V

Are you sure it is actually rated above 60A anyway? I think more discussion with the DNO is needed.
 
On a TN-C-S service where the L-N and L-E loop impedances are equal, surely Zs = 0.51Ω implies there will also be a problem for voltage drop?

Wow, exact simulpost with @pc1966!
 
Actually there is something more fundamentally wrong here. If it is TN-C-S then, unless there is something very bad at the cut out, the supply Ze is the same as the supply impedance. With 0.51 ohms and 80A you would be seeing 40.5V drop in the incoming supply! That is more than the ESQCR limits of +10% -6% on 230V

Are you sure it is actually rated above 60A anyway? I think more discussion with the DNO is needed.
Ok so I may have a case then..... assuming DNO have to comply with ESQCR? (not something I'm familiar with being honest)

Its got to be above 60a (for size of property) going to get the Client to dig out the original paperwork from when had it installed.
 

Reply to High Ze causing headache ! in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock