TheCodboy
Hi all, Doing some pre board change testing and ive found 2 sockets with high Zs readings. Everything else is fine, done all my end to ends and the Zs's are what should be expected. A couple of the sockets have Zs lower than expected but 2 are higher. They should be about 0.8 ohms but ive got one at 1.20 and one at 1.40. Taken the highest value socket off, re terminated, still high. Tested at the terminals of the socket just in case the socket was duff, but still high. Its a PME system with a good low ZE (0.15). Any thoughts people??
If you do end to ends at these sockets with a higher Zs reading, and you don't get continuity, then this socket will more likely to be a spurred socket. Importance of doing dead tests in the correct order. Although understand what you were trying to achieve, pre CU change.
Edit, as suggested by the other chaps!
TheCodboy
Newcastle
High Zs value with 2 sockets
TheCodboy,
TheCodboy,