13amp FCU off ring main supplying sockets in shed.
Zs at furthest socket in shed is 1.26ohms which is too high for a 32 amp mcb.
Would you use the 13amp fuse in the FCU to meet your Zs reading?
Zs at FCU is 0.70.
I understand your logic i.e. what's the difference between have a socket with a 13A extension reel going into vs a FCU with 13A fuse and long "extension" out to garage.
However difference is fixed vs non-fixed wiring. For fixed wiring then I think you already know the answer. So I would personally be looking to (depending on cost and longer term plans):
1. increase size of cable from FCU to sockets in garage, to reduce Zs to within acceptable limits.
2. or run a separate circuit for the CU to the garage with acceptable Zs for that circuit.
I know it's not ideal, but keeps you right.
Cheers @davesparks Guess I'm belt and braces type of guy.It is protected by the 13A fuse so needs to meet the Zs requirement for the 13A fuse.
[automerge]1592384713[/automerge]
It is protected by the 13A fuse so it is fully compliant and nothing needs to be done.
Cheers @davesparks Guess I'm belt and braces type of guy.Always thinking worst case and looking at potential changes down the line....
Agree with you fullyWhat worst case are you looking at here?
And what potential change?
We cannot protect against potential changes down the line because we cannot know for certain what will, or will not happen in the future.
Definitely can't see into the future, just what I've seen happen over the years, always plays at the back on my mind e.g. FCUs swapped out for sockets, fuses in FCU replaced by screws/wire.
Has RCD protection as well.
Most answers confirming what I thought with it being ok but have heard mixed opinions on this before.
If it's 30ma RCD protected at the origin of the final circuit the maximum permitted Zs is 1667 ohms. If it's not, it's supplying sockets, why isnt it?
Agree with you fully
Definitely can't see into the future, just what I've seen happen over the years, always plays at the back on my mind e.g. FCUs swapped out for sockets, fuses in FCU replaced by screws/wire.
No matter what we try to protect against (perceived or real) something will always be missed, hence evolution of the regs over the years.
Hope that makes sense? Apologies if I've inadvertently offend you, certainly was not my intention.
To add , the live conductors need checking against the formula T= K2 S2/I2 , the resulting number is how long it takes for damage to the live conductors to occur, nothing to do with whether the earth fault loop impedance complies or not.Need to be a little bit careful when applying this.
Yeah, this method then moves the job of earth fault protection from the OCPD to the RCD as the fault current is not enough to operate the OCPD quickly enough. The OCPD will still be covering short circuit protection so this then needs to be checked. If cpc is reduced size then probably ok as the fault current will be higher across live conductors, but you will still need to verify this is satisfactory. If you have situation where cpc is same size as live conductors and it wont satisfy Zs then it also won't satisfy live conductor thermal constraints either as will be the same fault current.
[automerge]1592523436[/automerge]
Seriously mate, I would not worry about what other people do in the future. If they make changes to an electrical installation then they are responsible for them.
Great point.Need to be a little bit careful when applying this.
Yeah, this method then moves the job of earth fault protection from the OCPD to the RCD as the fault current is not enough to operate the OCPD quickly enough. The OCPD will still be covering short circuit protection so this then needs to be checked. If cpc is reduced size then probably ok as the fault current will be higher across live conductors, but you will still need to verify this is satisfactory. If you have situation where cpc is same size as live conductors and it wont satisfy Zs then it also won't satisfy live conductor thermal constraints either as will be the same fault current.
[automerge]1592523436[/automerge]
Seriously mate, I would not worry about what other people do in the future. If they make changes to an electrical installation then they are responsible for them.