Hmm. Not entirely correct. I've just looked it up in the BGB. Section 522.8.10 seems to be the relevant bit:
"Except where installed in a conduit or duct which provides equivalent protection against mechanical damage, a cable buried in the ground shall incorporate an earthed armour or metal sheath or both...."

That's what I said innit? Gotta be in galv conduit or have an earthed sheath???? Maybe I should have been clearer, I should have said for any cable to be directly buried it needs earthed metallic protection.
Now, this only refers to protection of the cable against damage, not protection of diggers against electric shock (which is interesting).

If you were burying your cable in areas that were gonna have diggers mashing up the earth on a regular basis then galv conduit simply wouldn't be suitable mechanical protection.

I might contend that a piece of Hi-Tuff lying in the bottom of a proper length of ducting would be safer from mechanical damage than a piece of 2.5mm² SWA lying in the ground. After all, the armour of small SWA cable won't stop the cable being damaged if hooked up on the bucket of an excavator or even just chopped with a spade.

The armour of SWA is not really there to protect the cable from damage, it is there so that upon being damaged there is an immediate fault path to earth. Without the armour, Mr Jones could easily plant his spade through a line conductor but not neccessarily sever a neutral or earth. This is the whole point of SWA, a point many seem to forget.
 
Maybe I should have been clearer, I should have said for any cable to be directly buried it needs earthed metallic protection.

Absolutely, if directly buried (not in a duct), then SWA is the obvious cable to use.


If you were burying your cable in areas that were gonna have diggers mashing up the earth on a regular basis then galv conduit simply wouldn't be suitable mechanical protection.

By 'diggers', I meant blokes with spades!


The armour of SWA is not really there to protect the cable from damage, it is there so that upon being damaged there is an immediate fault path to earth. Without the armour, Mr Jones could easily plant his spade through a line conductor but not neccessarily sever a neutral or earth. This is the whole point of SWA, a point many seem to forget.

Yes, I quite understand that, in practice, having an earthed armour is A GOOD THING, for the reason you've stated. However, I contend that, if I choose to run my unarmoured, but otherwise suitable, cable (e.g. Hi-Tuff) in a robust plastic cable ducting which provides MECHANICAL protection at least as good as the armouring on SWA, then I think that the regs allow me to do this.

Now, I can see that there may be some debate about comparing the mechanical protection afforded by a particular ducting in comparison with SWA, but that doesn't negate the principle.
 
By 'diggers', I meant blokes with spades!

Haha, fair enough lol

I contend that, if I choose to run my unarmoured, but otherwise suitable, cable (e.g. Hi-Tuff) in a robust plastic cable ducting which provides MECHANICAL protection at least as good as the armouring on SWA, then I think that the regs allow me to do this.

Now, I can see that there may be some debate about comparing the mechanical protection afforded by a particular ducting in comparison with SWA, but that doesn't negate the principle.

I think this is where we disagree, for the simple reason that if I shoved a spade part way through an SWA the spade would be earthed before it severed a live conductor. If I shoved my spade part way through some plastic ducting and half way in to the NYY within then potentially I'm toast!

Some may respond with "how likely is it that you are only going to go part way through a cable", well my response is 'very!'. On Wednesday I will be replacing some garden lights for an old dear up my road because she did just this! Planted her spade half way through some buried pond flex and only severed the line conductor. I'm guessing it was only the plastic handle on the spade that saved her life.

My take on 522.8.10 is that unless you can protect a buried cable from penetration full stop (the seriousness of such potential penetration would have to be subject to risk assessment of course) then a cable encorporating an earthed metallic sheath is the only option.

Phew, all this talk of penetration is making me want to start harrassing the missus!
 