Octopus
If I was burying Hituff in conduit, it would be plastic, not metal!
Hmm. Not entirely correct. I've just looked it up in the BGB. Section 522.8.10 seems to be the relevant bit:
"Except where installed in a conduit or duct which provides equivalent protection against mechanical damage, a cable buried in the ground shall incorporate an earthed armour or metal sheath or both...."
Now, this only refers to protection of the cable against damage, not protection of diggers against electric shock (which is interesting).
I might contend that a piece of Hi-Tuff lying in the bottom of a proper length of ducting would be safer from mechanical damage than a piece of 2.5mm² SWA lying in the ground. After all, the armour of small SWA cable won't stop the cable being damaged if hooked up on the bucket of an excavator or even just chopped with a spade.
Maybe I should have been clearer, I should have said for any cable to be directly buried it needs earthed metallic protection.
If you were burying your cable in areas that were gonna have diggers mashing up the earth on a regular basis then galv conduit simply wouldn't be suitable mechanical protection.
The armour of SWA is not really there to protect the cable from damage, it is there so that upon being damaged there is an immediate fault path to earth. Without the armour, Mr Jones could easily plant his spade through a line conductor but not neccessarily sever a neutral or earth. This is the whole point of SWA, a point many seem to forget.
By 'diggers', I meant blokes with spades!
I contend that, if I choose to run my unarmoured, but otherwise suitable, cable (e.g. Hi-Tuff) in a robust plastic cable ducting which provides MECHANICAL protection at least as good as the armouring on SWA, then I think that the regs allow me to do this.
Now, I can see that there may be some debate about comparing the mechanical protection afforded by a particular ducting in comparison with SWA, but that doesn't negate the principle.