Just a quickie fellas..

Why am i not able to source any hituf cable from anywhere.. ?
TLC were listing some but now all gone..
Theres one or two on ebay but i would never buy cable off ebay..!!

Most electrical factors such as edmunson, CEF, etc just role their eyes in their head when I ask for it and say "Whats that?"
The next thing they say is "you want armoured mate"..

CEF seem to do a similar spec which they call "tuf-sheathed Non Armoured".. but do they 'ellers like keep any of it on the shelf..!

Anyone bought some recently.?
 
yeah thanks telectrix..
was hoping to avoid going mail order..
and was wondering why so many electrical "factors" are oblivious to it..! lol
 
NYY-J is the cable type, Hi-Tuff is a brand of NYY-J. TLC stock loads of NYY-J, in fact I've got about 150m of 2.5mm 5 core NYY-J left over in my garage from the last job I used it on. Usefull stuff :)
 
yeah thanks telectrix..
was hoping to avoid going mail order..
and was wondering why so many electrical "factors" are oblivious to it..! lol

So why don't you show your location in your profile - you never know there may be a wholesaler close by
 
Anywhere outdoors that won't be subject to severe mechanical stress. The last job I used it for was in a marina as it is rated for underwater use.
 
Thanks, i'm presuming when its still protected by RCD? rather than using non-RCD'd SWA to save expense for example?
 
Thanks, i'm presuming when its still protected by RCD? rather than using non-RCD'd SWA to save expense for example?

No,an RCD is no substitute for adequate mechanical protection. You may or may not need an RCD on a circuit fed using SWA, the same applies to NYY-J. In short, if the cable needs mechanical protection, being buried is one example, then it needs to be armoured.
 
Thanks chaps.

What are your views on using Hi-Tuff in underground ducting instead of SWA buried direct? It's more expensive that way, but on the odd occasion it might suit, due to its smaller dimensions, or where numerous ends need to be made off.
 
If the ducting encorporates an earthed metallic sheath then why not. Galv conduit of galv flexi would be fine but SWA is always preferred.

The crux of the matter is that for anything to be buried it has to encorporate earthed metallic protection.
 
If the ducting encorporates an earthed metallic sheath then why not. Galv conduit of galv flexi would be fine but SWA is always preferred.

The crux of the matter is that for anything to be buried it has to encorporate earthed metallic protection.

Hmm. Not entirely correct. I've just looked it up in the BGB. Section 522.8.10 seems to be the relevant bit:
"Except where installed in a conduit or duct which provides equivalent protection against mechanical damage, a cable buried in the ground shall incorporate an earthed armour or metal sheath or both...."

Now, this only refers to protection of the cable against damage, not protection of diggers against electric shock (which is interesting). I might contend that a piece of Hi-Tuff lying in the bottom of a proper length of ducting would be safer from mechanical damage than a piece of 2.5mm² SWA lying in the ground. After all, the armour of small SWA cable won't stop the cable being damaged if hooked up on the bucket of an excavator or even just chopped with a spade.

Is there something else in the regs that I'm not spotting?
 