R

rob22591

hi there. was at a job today and the previous electrician has wired a hob in 4 core 2,5mm swa (with separate earth) it is wired in a 3 phase setup with each core being on a 16amcb. as it is a single phase db and setup. is this safe. hob needs a 32asupply
thanks
rob
 
hi there. was at a job today and the previous electrician has wired a hob in 4 core 2,5mm swa (with separate earth) it is wired in a 3 phase setup with each core being on a 16amcb. as it is a single phase db and setup. is this safe. hob needs a 32asupply
thanks
rob

what is the make/model of the hob?
 
You sure you have check that right? As that is not 3 phase that is just 3 seperate lines of the same phase run to the same place. Just technically a 7.5mm cable as its 3 parallel cables and a 2.5 neutral to the same place.
 
hi there. was at a job today and the previous electrician has wired a hob in 4 core 2,5mm swa (with separate earth) it is wired in a 3 phase setup with each core being on a 16amcb. as it is a single phase db and setup. is this safe. hob needs a 32asupply
thanks
rob

No that is neither safe not compliant, you cannot have a single neutral conductor which is shared by multiple final circuits. For 3x single phase supplies there must be 3x neutral conductors.
The neutral is potentially overloaded as it is at the moment.

Get the installers name and details and report them to anyone who will listen, trading standards, the scams, HSE or anyone else
 
He cant of possibly been an electrician.....The manual says the overall power consumption can be reduced to 4.4KW and minimum circuit breaker size is 20A. Depending on the installation method of the SWA you could put it on a 20A circuit breaker, use three of the cores as LNE and tie the last core down to earth, ditch the separate CPC and make sure the SWA is glanded appropriately with at least one end connecting the armour to earth.
 
Totally agree with Dave that should be a linked triple-pole device not three separate ones.
 
He obviously lost the supplied links for the 230v set up.....
As above it isn't safe or compliant.
Name and shame!


Sent from my iPhone using Tapatalk
 

OFFICIAL SPONSORS

Back
Top