Well check out 3.6.1 In the on site guide on P(21-22)...for TT systems ALL circuits must be given RCD protection mate and the only way to get discrimination would be tu use an s type ...upstream of the outbuilding feed.....which would then feed another RCD at the outbuilding end............

Really best to check out Regulation 411.5.2
 
Why wouldnt you just take a supply from a spare way in the C/U to an outbuilding because the chances are you would have to take the cable through places that need 30mA protection anyway. I can understand the need for a time delayed RCD on a TT if the C/U was a distance from the cutout and you had to run a submain.
 
Why wouldnt you just take a supply from a spare way in the C/U to an outbuilding because the chances are you would have to take the cable through places that need 30mA protection anyway. I can understand the need for a time delayed RCD on a TT if the C/U was a distance from the cutout and you had to run a submain.

... because when the RCD trips, you'll be in an outbuilding 100 feet away from the RCD. Thats why ...? It's damned inconvenient and potentially dangerous (e.g. middle of winter, elderly person, dark, raining). .... ?
 
An if the RCD doesnt trip they still have to walk 100ft back to the house, in the dark, in the rain and in the middle of winter anyway!
 
100mA would only be used to protect tails if was a distance from cutout to cu.... fire aswell ????? whats the maths with this, i know it shouldnt be ore than 300mA, is 300mA the edge of fire tempeture or something...
 