Wanted to look up what 1mm flex is rated for when run in trunking but couldn't find it listed, just it's rating in free air.

You'd think flex inside trunking would be fairly commonplace, especially in offices in dado trunking etc. but also in commercial/industrial where the use of trunking is widespread.

Anyone know the reason for the omission?
 
Because it wouldn't be it's normal installation method. Flex is not commonplace for fixed electrical installations.
 
Because it wouldn't be it's normal installation method. Flex is not commonplace for fixed electrical installations.
I do see it with fuel tanks. Someone will have initially run a length of trunking instead of some tray and every addition thereafter goes in it. Usually alarms, gauges and other low current equipment that needs mounting on the wall of the tank.

It can't just be in those instances though, I'd have thought it was common in other industrial areas.
 
Saying it is not commonplace doesn't mean it doesn't exist in these settings but would not be the first choices. Your instances suggest it is not being installed by more kitted out electricians, they have flex and that is what they use.
 
Saying it is not commonplace doesn't mean it doesn't exist in these settings but would not be the first choices. Your instances suggest it is not being installed by more kitted out electricians, they have flex and that is what they use.
I don't really know what else could be used, apart from the H07 rubberised flex stuff. Singles wouldn't work as it needs to leave the trunking and wire into the unit itself, and these units don't accept SWA or SY glands, which would be overkill anyway where there's already mechanical protection.

If it was me doing it from scratch I'd use tray but where trunking is used then flex seems the best option for these applications. I do understand that this is a pretty niche scenario, but there's plenty of those accounted for in the brown book.
 
If these cables are being used for low current applications then calculations are probably academic as 1.0mm² will take 10A in free air. As alternative you could use singles in trunking and fit fuse connection units then install your flex from there.
 
If these cables are being used for low current applications then calculations are probably academic as 1.0mm² will take 10A in free air. As alternative you could use singles in trunking and fit fuse connection units then install your flex from there.
Yeah I just wanted to make sure running it in trunking wouldn't derate the cable under the 6A MCB. I guess table F3 would basically do the same thing, as it accounts for multi core cables being embedded or enclosed.

As for the fused spur idea, I think it would work in some instances but not this one as there's nothing to fix a fused spur back box to - could attach the bush and coupler to the top of the trunking but the backbox wouldn't be able to be fixed as that's the bund of the fuel tank itself.

Should mention that the units are all fixed to metal plates that are pre welded on when they're manufactured. Working in fuel tanks can be a pain for this reason as if everything is taken up you're then looking at taking it all down, adding unistrut and adding it all back again. Turning a simple install into a long one!
 