Most likely wont go with upfront rcd due to cost . I would rather not fit the spd to be honest due to the issues it brings up. But if customer wants it I want to make sure its done correctly. Also do I need to worry about the spd type with it being TT. And if so does anyone have a link to a suitible C.U with correct type
 
These are good, but not cheap, and they offer choices for TT and TN options:

But more generally the 1+1 style where you have one SPD element L-N and another from N-E you don't have any single point of failure that would allow a L-N short with all of the danger related to it. There are many cheaper options for that configuration, as it is common in the EU to have TT anyway.
 
Most likely wont go with upfront rcd due to cost . I would rather not fit the spd to be honest due to the issues it brings up. But if customer wants it I want to make sure its done correctly. Also do I need to worry about the spd type with it being TT. And if so does anyone have a link to a suitible C.U with correct type
If you look at the fuseboard prices any additional costs would be minimal. If such costs are making such a dent, with respects you are not charging enough.
 
If you look at the fuseboard prices any additional costs would be minimal. If such costs are making such a dent, with respects you are not charging enough.
it would be in a separate metal clad enclosure and the rcds are about 50 a pop. why pay it if its not necessary
 
I think you are over thinking things a little, use a proper tails gland and consider Wilko's suggestion and forget the separate enclosure.
 
I think you are over thinking things a little, use a proper tails gland and consider Wilko's suggestion and forget the separate enclosure.
ok that probably is the case as this will be my 1st inspection just need to make sure on the correct spd type never really thought about it before they have just gone straight in on tn systems.
 
In addition, rcd's / rcbo's have a tendency to fail when you don't want them to. As with TT they will not be additional protection I would definitely go with an upfront time delayed DP RCD. I do not believe you have to, but that would be my preference.
 
In addition, rcd's / rcbo's have a tendency to fail when you don't want them to. As with TT they will not be additional protection I would definitely go with an upfront time delayed DP RCD. I do not believe you have to, but that would be my preference.
ahh ok in replacement of the main switch wouldnt this mess with any spd tho as it would be down stream. but yes good shout
 
I've got to be honest, I'm not so sure about an SPD with TT unless you have a pretty good Ra - I will leave that for others to comment for now as off to bed :)
 
I've got to be honest, I'm not so sure about an SPD with TT unless you have a pretty good Ra - I will leave that for others to comment for now as off to bed :)
Most electronics is at risk from the L-N volts, so the (typical) MOV SPD covers that. The N-E will normally have a higher damage voltage, so the GTD is enough protection before cables flash over or class-Y filter capacitors go pop.

If you are TT on the end of a long rural cable you might want to look at the type 1+2 SPD that can divert a lot more energy, much as you would if the building has lightning protection. Usually though in the UK the flash density if fairly low.
 
Most likely wont go with upfront rcd due to cost . I would rather not fit the spd to be honest due to the issues it brings up. But if customer wants it I want to make sure its done correctly. Also do I need to worry about the spd type with it being TT. And if so does anyone have a link to a suitible C.U with correct type

A Fusebox time delay RCD is only about £40. If you are trying to contain the cost for the customer, just fit this out of your own pocket and regard it as "insurance" against NICEIC raising a problem not having one installed during your assessment. Also, the Fusebox SPD now sits after a 32A MCB (originally there was no MCB, but they changed that last year).
 