Darkwood

As 95% of my work is panel building and machine repair i actually use this forum to stop me falling behind with general installation regs... anyway was at a factory other day and he has his own sparky that has pre-installed a 5core 4mm swa to supply 3 steel containers they want lighting into and a small compressor supply.

As im doing my pricing at our lasses ive not got regs to hand so just clarify my thinking here pls.

The incoming supply is to a 3ph 4way Bemco TNCS and if i wanted to extend the existing equipotential zone to the steel containers i would need to run a 50mm earth with the existing swa thats been already run, this is now buried in concrete so not an option.

This leaves the only other option of isolating the swa earth at load end and TTing the install there onwards
Ive also instructed the owners that the existing equipotential bonding is undersized at 10mm and should be upgraded to 50mm to Gas, Water and Structural...

The reason i ask is he called this now retired sparky who insisted i was wrong and didn't know what i was talking about assuming to save face but although my confidence is high ive just having a blonde moment and questioning my insanity lol .... please point out if ive been a tithead here it has been known to happen to the best of us ;) when you argue who's correct sometimes you end up with a seed of doubt yourself.
 
i would have thought that the cpc does not need to be larger than the line conductors asa they both have to withstand the same fault current. table 54.7, with a bonding conductor a min. of 10mm for tNC-S.
 
Hi Dw,

where PME conditions apply, the minimum csa is sized in relation to the incoming Neutral of the supply* (*included for reference), taken from table 54.8 of the BGB is as follows:

N conductor to Main Bonding csa

35mm or less =10mm

over 35mm up to 50mm =16mm

over 50mm up to 95mm = 25mm

over 95mm up to 150mm = 35mm

over 150mm = 50mm

Edit; sorry for the poor formatting, I did try to space it out a bit better, but the forums software mangles the formatting. lol
 
Last edited by a moderator:
Cheers boys just aint got my book yes main earth is 70mm that i remember due to Incoming L csa- -- it the equipotential bonding i cant remember if i extend the equipotential earth zone to the steel containers then a DNO N fault may see the current flow the alternative route through the containers down the equip bond back to service head are vice versa dependent on fault location... with this in mind it would require to be able to handle the high currents associated with the supply thus a 10mm would just overheat and melt, so without table to hand i estimate it has to be equivalent to be 50mm ish and looking at table SPARK68 i hit nail on head.


This isn't about an installation fault where suitable fusing limits current flow its about 'circulating currents' associated with broken DNO neutral which in industrial areas can be very high.

Actually i best contact DNO as they can command a higher csa dependent on the size of the local network.. i once had to run a 95mm^2 at there demands.
 
Last edited by a moderator:
I just gave you the the main equipotential bonding sizes above DW, :wink_smile: although I was editing it as you were posting, lol I was faffing around to improve the layout, bloody computers lol (or operator error lol)

I was just about to add that the DNO may have more stringent requirements over and above to the minimum given in the table, it is in a note at the top the table I gave the information from, but I see you beat me to it.
 
Last edited by a moderator:
Sorry saw your reply after posting Sparks' but cheers sorted and i was correct all along hence ive since edited it to suit cheers again... still will ring DNO to confirm as i really should be upgrading existing bonding to suit.

The Steel Containers are been TT'ed so can go ahead and make a start while they take 6 months to tell me no special requirements from their network lol
 
but if there was a loss of the DNO neutral, any current flow through the cpc of the SWA would be limited by the OCPD of the 4mm SWA.
 
Tel its a combined E/N on DNO side if it was lost it would use local equipotential bonding as a path and as you dont fuse the earth it would see very high circulating current flow hence the different criteria for pme supplies ...this is external current source from the pme network not the current running down the swa supply to the containers thats not why these regs exist with regards bonding conductors in tncs supplied systems.
 
ah, i was considering the cpc, not the bonding. however, would a large proportion of the current not flow in the installation neutral back as far as to the point where the N and E are combined? it's a concept i struggle with to visualise.
 
Ill try explain to simplify... consider a DNO network with 3 installations A B and C each with a 400amp supply on TNCS from the same sub station... if A is the first in the supply line then B then C then consider a pme fault between B and C in that the N/E is lost the current may track through the true ground to any equipotential bonding in B to its DNO incomer to maintain it circuit and been industrial this can be hundreds of amps now if in my case i earthed my steel containers with the 4mm earth in the cable it will find this path with a massive current flow and burn it out ...

Its known as a circulating pme fault current and if the network has local bigger supplies to other local buildings then the DNO can command a bigger bonding than the max 50mm earth you might use according to the BS7671 to carry the possible network fault current...

Does this make sense Tel?
 
Last edited by a moderator:
it's becoming clearer.when i've got me head on, i'll draw it out. probably be obvious then. cheers.
 