Hello, I’m in dire need of help.
here is the question

A kitchen Ring final circuit is wired in 2.5/1.5mm T&E and protected by a 32A type B circuit breaker. 70m of cable has been used.

Q1. What is the expected r1, r2, rn value ?

So far I’ve used the equation R=Mohms/m X Length =1,365.7 divided by 1000 = 1.36

what do I do with this number 1.36 to get the values ?
 
You will need to consider the resistance per metre of the line / neutral and CPC separately as they are of different CSA.
 
One can either look up the resistance per unit length in a table or calculate it from the resistivity (ρ) of copper. For normal cables made to recognised standards such as T+E, I would suggest looking it up. Construction tolerances might make the tabulated value fractionally different from the theoretical minimum.

And @stevethesparks whilst I know what you mean by:
2.5 = 0.49
Its blatant falsehood as a mathematical expression gives it an air of naughtiness that we should not encourage amongst students! I would rather write longhand 'Resistance of 2.5mm² conductor = " etc.
 
One can either look up the resistance per unit length in a table or calculate it from the resistivity (ρ) of copper. For normal cables made to recognised standards such as T+E, I would suggest looking it up. Construction tolerances might make the tabulated value fractionally different from the theoretical minimum.

And @stevethesparks whilst I know what you mean by:

Its blatant falsehood as a mathematical expression gives it an air of naughtiness that we should not encourage amongst students! I would rather write longhand 'Resistance of 2.5mm² conductor = " etc.
Thankyou very much guys ! I enjoyed reading over the last part of that reply in particular. ?
 

Reply to I need help with figuring out an equation in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Need help check that my cable calculations are correct as still new to doing them. 6A Lighting Circuit 60898 MCB Type B wiring in 1MM²/1MM² T+E...
Replies
13
Views
3K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hey there, Sorry I’ve just joined up. I’m a qualified electrician/Electrical engineer. Recently sat my 2391-52. My question is I had a fault...
Replies
4
Views
1K
Hi, and thank you to anyone who's taking the time to read my question. i'm struggling with the outcome of an adiabatic equation i'm doing and...
Replies
4
Views
3K
Hey all, i honestly cant work this out, i think its the way they ask the questions and am not sure whats going where, am failing on my maths like...
Replies
6
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock