Hello, I’m in dire need of help.
here is the question
A kitchen Ring final circuit is wired in 2.5/1.5mm T&E and protected by a 32A type B circuit breaker. 70m of cable has been used.
Q1. What is the expected r1, r2, rn value ?
So far I’ve used the equation R=Mohms/m X Length =1,365.7 divided by 1000 = 1.36
what do I do with this number 1.36 to get the values ?
You will need to consider the resistance per metre of the line / neutral and CPC separately as they are of different CSA.
One can either look up the resistance per unit length in a table or calculate it from the resistivity (ρ) of copper. For normal cables made to recognised standards such as T+E, I would suggest looking it up. Construction tolerances might make the tabulated value fractionally different from the theoretical minimum.
And @stevethesparks whilst I know what you mean by:
2.5 = 0.49
Its blatant falsehood as a mathematical expression gives it an air of naughtiness that we should not encourage amongst students! I would rather write longhand 'Resistance of 2.5mm² conductor = " etc.
Thankyou very much guys ! I enjoyed reading over the last part of that reply in particular. ?
Reply to I need help with figuring out an equation in the UK Electrical Forum area at ElectriciansForums.net
Need help check that my cable calculations are correct as still new to doing them. 6A Lighting Circuit 60898 MCB Type B wiring in 1MM²/1MM² T+E...
Hi, and thank you to anyone who's taking the time to read my question. i'm struggling with the outcome of an adiabatic equation i'm doing and...
I work in the events industry which works under 7909. This assumes that someone qualified 7671 etc has tested the distor's and designed a system...
Hello all, I was hoping for some advice on this ring fault I have come across. It has been intermittent for about 2 months now. It is a converted...