UPDATE! Found the fault. Tested between neutral and earth, however left cpcs in earth bar to see if it was shorting on another circuit or pipes. Tester showed dead short. Traced cables and found they run behind the boxing in for rad pipes. Took off rad cover and there it is in front of my eyes the leg that had been squished.... therefore shorting on to the neutral.... replaced leg of ring and re tested. All good. Must of been plumber who chsnged the stats on the rad cover and squashed the cable wheb putting the cover back. The reason it was tripping every so often was because there was a play centre cabinet for the kids and everytime the kids would push the cabinet it would push the rad cover into the neutral. IR reading are 10megaohms which is not that great but the cable run they have used goes under the floor after the boxing in. All is good now, thanks for everyones help! (Also attatched some pictures)
 

Attachments

  • A5598662-8D92-445B-91D2-5A470DF55189.jpeg
    A5598662-8D92-445B-91D2-5A470DF55189.jpeg
    1.4 MB · Views: 65
  • 0DD0EF8D-BF03-411C-8DAA-4C46FA048537.jpeg
    0DD0EF8D-BF03-411C-8DAA-4C46FA048537.jpeg
    1.5 MB · Views: 67
This is typical of a chewed or punctured cable where there's a tiny airgap between the conductors, large enough to not flash over during the IR test but small enough to short out when anything expands with heat or other minor disturbance happens.

Have you tried testing it at 1000V?
Thank you, disturbance was the kids unfortunately
 
looking at those pics.are you sure wet-pants didn't nail the cable after you'd questioned his parentage?
 
  • Like
Reactions: Pete999
UPDATE! Found the fault. Tested between neutral and earth, however left cpcs in earth bar to see if it was shorting on another circuit or pipes.
I don't mean to be unkind, but why did you test without the cpcs connected to the means of Earthing before? It is a requirement of the Wiring Regulations that they be connected when conducting the test.
 
  • Like
Reactions: 123 and DPG

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Intermittent Ring fault! Any advice please.
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
25

Advert

Thread statistics

Created
kmulcahy1994,
Last reply from
kmulcahy1994,
Replies
25
Views
3,518

Advert