Thank you, disturbance was the kids unfortunatelyThis is typical of a chewed or punctured cable where there's a tiny airgap between the conductors, large enough to not flash over during the IR test but small enough to short out when anything expands with heat or other minor disturbance happens.
Have you tried testing it at 1000V?
I don't mean to be unkind, but why did you test without the cpcs connected to the means of Earthing before? It is a requirement of the Wiring Regulations that they be connected when conducting the test.UPDATE! Found the fault. Tested between neutral and earth, however left cpcs in earth bar to see if it was shorting on another circuit or pipes.
Quite possibly! Hahalooking at those pics.are you sure wet-pants didn't nail the cable after you'd questioned his parentage?