Hi all , after some opinions on N-E fault or ring main.

After chasing this fault and ruining my bank holiday weekend , ring main IR readings as follows

L-E >999
L-N>999
N-E>0.98Mohm

I have narrowed it down to a cable spurred from ring main , astonishingly the 3no. Cables in the twin switched socket all individually test out at >999 across all conductors. It’s only when connected together that it causes the low reading , like there is a low resistance between 2 different cables ,any ideas?

TNCS supply , split load consumer unit
 
Try a wander lead from the MET to each of the 3 conductors at end of the spur, with the spur disconnected at the branch point.
It could be a damaged cable touching a pipe that is bonded.

Also check end-to-end ring integrity as a broken ring can upset otherwise sound logic!
Finally double check that when the spur is disconnected at the branch point and the other two cables wago'd together, there is no fault showing up back at the board.
 
Last edited:

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Staffordshire
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
N-E fault bank holiday ruined
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
3
Unsolved
--

Advert

Thread statistics

Created
MWD149,
Last reply from
westward10,
Replies
3
Views
1,614

Advert

Back
Top