andygosmore

Evening all - does anyone know if there is a regulation specifically requiring a distribution board to have something on it showing it's source - ie. where the submain that is supplying it is fed from? I'm testing a large school with 80+ boards, and not many show source.
And, a totally seperate question, what do people think of running a circuit (in this case a pump) through the enclosure of a heating panel. fed from a totally seperate circuit?
Thanks
Andy
 
1, would probably be your recomendation to install signage in remedial works after testing etc

2, suppose it depends if the pump is anything to do with the heating even though on different circuit
 
Re the pump, you would have to make sure that (if it is single phase) the phase on the pump and the phase on the boiler are the same phase, or you will have a potential 415 v shock voltage inside what looks like a 240v unit.

Phil
 
re the pump the wiring should go dead when the other wiring does or there should be a warning label stating 2 different supplies exist within this enclosure.
 
Evening all - does anyone know if there is a regulation specifically requiring a distribution board to have something on it showing it's source - ie. where the submain that is supplying it is fed from? I'm testing a large school with 80+ boards, and not many show source.
And, a totally seperate question, what do people think of running a circuit (in this case a pump) through the enclosure of a heating panel. fed from a totally seperate circuit?
Thanks
Andy

Have a look at Regulation 514.9

Dichroic
 

Reply to Identifying supply source in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Good morning all, I am currently working on a House in Multiple Occupation (HMO) consisting of 10 flats, with three parking spots equipped with...
Replies
9
Views
605
Hi all, Merry Christmas to everyone, and apologies for talking work during the holidays😅 I have my first EV charger install job early in the New...
Replies
14
Views
2K
Was having a poke around the old man's house today. Anyway. DB is under stairs (18th ed following a recent extension. Not done by me but it's...
Replies
7
Views
785
Hello everyone, I am currently in the process of estimating the electrical demand for a new construction development that will consist of an...
Replies
0
Views
873
We have had builders in, who have stopped for Xmas. My daughter tried to do a wash. The wash machine wouldnt. Its power socket is dead. I...
Replies
4
Views
708

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock