guys,

got a customer that wants to change there oven but only has a 6mm cable oven is on a 3 pin plug so 13amps but the hob in 6200 watts how to i convert this to kw or amps and would both units be ok on a 6mm with a 32amp breaker.

thansl
 
guys,

got a customer that wants to change there oven but only has a 6mm cable oven is on a 3 pin plug so 13amps but the hob in 6200 watts how to i convert this to kw or amps and would both units be ok on a 6mm with a 32amp breaker.

thansl
Are you kidding? 6200 watts is 6.2 kw 6200/230 =26.95 but you apply diversity to that but you know how to do that?
 
mate have'nt done it in so long can you help me out

Ok bud, 1000 watts is 1kw so 6200 watts would be 6.2kw, you take your 6200 watts divide by the voltage 230 = 26.95 amps but then apply diversity 10 amps +30% of full load after 10 amps so 10 amps+8.1 +5amps if there is a socket in the cooker isolator so it'll be either 18.1 amps or 23.1 amps depends on whether you have a socket;) 32 amp will be fine on 6mm cable
 