A
adderzigzag
Sorry to post such a long message but realise people need all the information so accurate conclusions can be reached. The domestic property has a supply feeding some out building via three core cable from the house protected by a B40, more on that later! The supply to the house is single phase TN-CS (PME), this may also be relevant later!
I was called to help out with a problem on a tripping breaker in the house feeding the outbuildings, at that time it was a B40 RCBO (30mA) for obvious reasons. It was established that within the outbuildings the client had fitted a Sauna, a little look at Section 703 mentions RCD protection should NOT be fitted to the heater supply unless otherwise stated by the manufacturer.
Clearly the heating elements are inherently leaky and an Insulation Resistance Test confirmed that.
An IR test on the cable proved satisfactory.
I recommended a split consumer unit to be fitted in the outbuilding, change the feed breaker within the house from RCBO to straight MCB. Both have the same overcurrent rating.
The split board was then configured to provide a non-RCD supply to the heater with all other circuits on the RCD side.
A Zs was measured at a 13A socket outlet in the outbuilding at 8 ohms, not good for a B32 breaker 1.15 ohms max tabulated, however RCD was upstream considering this high earth fault loop impendence, think max is 1667 ohms, with RCD.
With some further investigation the 3 core cable to the outbuilding did not have the CPC connected to earth at the MET within house DB nor was the SWA connected, at the very least one end should be bonded as this is an exposed conductive part.
When questioning the client he said the installer said under no circumstances should this core be connected to the MET, outbuilding end is also unearthed. There is an earth rod at the outbuilding and the structural steel work also bonded.
OK my question and I know there are issues using PME with various Special Locations, like caravan parks, farms, marinas, plus others.
Why should the cpc on the feed cable not be connected at the MET at the outbuildings DB? This would drop the Zs dramatically to the outbuildings and hence aid disconnection time issues. So should I connect it or not? What would be the negative consequence of connecting it? Is it a PME ruling?
Look forward to any suggestions as currently the disconnection time on the feeder cable is likely to be pretty rubbish even considering it would be a 5s disconnection!
Hopeful for some good suggestions