Can someone point me in the direction of the Reference Method for a cable which is lying on top of, but not enclosed in thermal insulation.

In my loft all the cables are laid on the insulation. I'm installing a larger storage heater so want to check the current 2.5mm T+E is up to the job.
 
Do not have my bgb to hand, but if it was sat on top of insulation I would consider it as clipped direct. For that part of the run anyway, depends on how it gets to the fcu/dp sw for the heater.
Hope this helps
 
The drop to the DP is through the cavity behind insulated plasterboard. Ref Method 102.

For some reason, the OSG, the Guide to Building Regs and the green book make no reference to cable that is sitting on top of insulation.

I'd usually use the next worse case scenario (method 103) but in this case it would mean I'd have to upgrade the whole cable to 4mm.
 
i would say method c mate...but as above...will depend on how it arrives at the heater....
 
Seems very odd that there's no mention of it!

Even though it's not an ideal method, millions of homes have cables run over the loft insulation, so you'd have thought there would be a specific mention of it in the books!
 
If its run on top of insulation it is not really different to running on top of anything else. Still surrounded by air on the majority.
 
i think they just use method c to cover it....at least its better than after MR numpty has come along with his rockwool and just thrown it all over your cables..lol.....
 
I'll go with the 2.5mm, but clip it to the joists wherever possible.

Even if it was enclosed completely, it would still be very close to be compliant (14.5A max draw, up to 13A permissible) so can't imagine it being a problem.

Cheers for the help guys
 
There is no requirement to clip the cable as long as it is supported through its length. This could be lying on a surface. I.e the insulation.
But clipping would be better practice.
 
There is no requirement to clip the cable as long as it is supported through its length. This could be lying on a surface. I.e the insulation.
But clipping would be better practice.
hmm...i think i might be clipping this mate.....
 