Discuss Insulation resistance for devices in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

Reaction score
1
I was checking the IR on a socket circuit and found 0.4M between neutral/earth. The reading came from a garage door motor that was plugged in. once unplugged the IR was good. Does the circuit need to be cleared of all things plugged in when testing or does this constitute as a fault. I was called to do this due to spurious RCD tripping.
 
You are only testing the fixed wiring unless you are also being contracted to carry out portable appliance testing. Another reason to unplug everything apart from the obvious false test results is you could damage some electrical components while IR testing.
 
I was checking the IR on a socket circuit and found 0.4M between neutral/earth. The reading came from a garage door motor that was plugged in. once unplugged the IR was good. Does the circuit need to be cleared of all things plugged in when testing or does this constitute as a fault. I was called to do this due to spurious RCD tripping.
When I'm fault-finding a tripping RCD, I leave all equipment in circuit for the initial test, and remove piece by piece to see the effect it has on the IR.

0.4M ohm is a typical IR reading for SPDs. If you get 0.4M ohm at 500V but much higher at 250V, there's a good chance that it's due to surge protection. Was IR L-E acceptable?
 
0.4M between neutral/earth. . I was called to do this due to spurious RCD tripping.

Obviously that in itself won't cause tripping, the IR would need to be 1000 times lower to leak a reasonable number of milliamps from neutral to earth under typical conditions. Even 0.4 megohms L-E is still 30 times higher than would cause a trip.

When testing current-using equipment, the test really ought to be between both L+N paralleled to earth, just as a PAT tester does it, regardless of whether the equipment is portable or hard-wired. As mentioned above that is quite a common result for VDRs tested at 500V and there might be a VDR in the door motor.
 
There's very little voltage between N & E under normal conditions. Assume the circuit is running at something near maximum voltage drop of say 10V (4.3% of 230V) therefore there is 5V drop along the line conductor and 5V along the neutral. If we also assume that whatever is causing the IR is located in the worst place so that the 5V appears across that 0.4MΩ, then it's just ohms law and the leakage would be 5/0.4M = 12.5μA. I.e. so tiny that it's completely swamped by normal functional leakage. Even with a resistance 1000 times lower, at just 400 ohms, the worst-case leakage would still only be 12.5mA and less than the tripping threshold, and that's with 5V between N & E. Near the board on a TN-C-S supply, the drop might only be a fraction of a volt, in which case it is going to take a lower resistance still, perhaps just ten ohms or less, before it trips. That is how even solid neutral-earth faults can lie low until there is enough load on the system to drive up the N-E voltage.

Obviously if the low IR is located L-E instead then the leakage is 230/0.4M = 0.6mA. With no other leakage sources, a typical RCD that trips at 22mA would need a resistance below 230 / 0.022 = 10.5kΩ to trip it. This can be disconcerting when reading the IR on digital display that shows nnn.nn MΩ. The display can legitimately show 0.00 MΩ and yet the insulation is still high enough to not trip. Only by going to a higher resolution do you see the difference between say 12kΩ which probably won't trip, and 2kΩ which will.
 
There's very little voltage between N & E under normal conditions. Assume the circuit is running at something near maximum voltage drop of say 10V (4.3% of 230V) therefore there is 5V drop along the line conductor and 5V along the neutral. If we also assume that whatever is causing the IR is located in the worst place so that the 5V appears across that 0.4MΩ, then it's just ohms law and the leakage would be 5/0.4M = 12.5μA. I.e. so tiny that it's completely swamped by normal functional leakage. Even with a resistance 1000 times lower, at just 400 ohms, the worst-case leakage would still only be 12.5mA and less than the tripping threshold, and that's with 5V between N & E. Near the board on a TN-C-S supply, the drop might only be a fraction of a volt, in which case it is going to take a lower resistance still, perhaps just ten ohms or less, before it trips. That is how even solid neutral-earth faults can lie low until there is enough load on the system to drive up the N-E voltage.

Obviously if the low IR is located L-E instead then the leakage is 230/0.4M = 0.6mA. With no other leakage sources, a typical RCD that trips at 22mA would need a resistance below 230 / 0.022 = 10.5kΩ to trip it. This can be disconcerting when reading the IR on digital display that shows nnn.nn MΩ. The display can legitimately show 0.00 MΩ and yet the insulation is still high enough to not trip. Only by going to a higher resolution do you see the difference between say 12kΩ which probably won't trip, and 2kΩ which will.
Thanks I’ll pour over that Boxing Day. Merry Christmas to you all.
 

Reply to Insulation resistance for devices in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

Similar Threads

Hello all, I hope you're all keeping well. I have a question regarding insulation resistance testing. Whether doing a single circuit IR test or...
Replies
9
Views
522
During an insulation resistance test IR at an EICR I measured 0.0014 MegOhms from line to earth. When I disconnected the neutral from the neutral...
Replies
4
Views
1K
Hi all, We have a limited in house PAT testing requirement and were advised that the TIS700 fitted our needs. The unit works fine for 110V and...
Replies
0
Views
621
I want to check the insulation of the 3-phase 400VAC asynchronous squirrel cage motor. Motor's stator windings are connected in delta. I've read...
Replies
10
Views
2K
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
727

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock