Evening all.

I have been asked by a Company, to install the feeds to a new intelligent lighting system for a customer. The system will be installed by the separate company.

Having spoken to them, I understand how the feeds differ from a conventional radial circuit, my issue is the initial testing. The feeds from 2 or 3 MCB's at the CU, go out via a module for the lighting system, to each of the legs being controlled.

Is it as simple as choosing the circuit within the specific MCB and measuring this for each and every leg? Pardon my ignorance please.
 
It very much depends on the particular lighting system. We've installed DALI systems where all the light fittings are supplied directly on a radial and they're all independently addressable on the comms side from the central control. I'm not sure how your system is configured but it sounds different.
 
OK......I'm going to make a guess here as there's several possible options. You've got a feed from the source > [control box/dimmer being installed by others] > lights on cables 1st fixed by you.

You do the normal collection of tests on anything that will have 230 applied to it, and ignore everything else.
 

Reply to Intelligent Lighting in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi Guys I've fitted a few emergency lighting circuits to both domestic and commercial installs before, I've come across one I can't get my head...
Replies
19
Views
1K
Hi guys, I have supplied my Shed with a 6mm SWA cable into a nice consumer unit. In there I have a 6Amp MCB for the lights and a 16 A supplying a...
Replies
25
Views
932
I live in a warehouse condo, converted about 20 years ago. The building dates to about 1870 but with the conversion, all of the electrical was...
Replies
3
Views
478
Hi I'm in need of some advice. First of all i'm not an electrician but do have an understanding of electrics as i come from an electronics...
Replies
4
Views
607
Old two core cable in a lighting circuit with no cpc at any point All points had metal fixtures and fittings class1 At two points the live loop...
Replies
0
Views
613

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock