- Reaction score
- 3,010
Had a call out at a dental practice at 19:00 last night in the end I left the fault disconnect requiring further investigation.
This fault not the simply resolved call out fault but a "while you're there can you look at" Friday night special.
Very bizarre set up as the building looks to be a rather small corner terrace, two up two down, with a large single storey rear extention yet, just inside the front door is a three phase supply with one phase in use (supply 1 feeds DB1 & DB2) then in the rear room of the original build is a second three phase supply again with one phase in use (supply2 feeds DB3), both L3.
The "while you're there" fault I was looking at was an extractor fan that tripped when turned on.
The fan was fed from a B32 MCB, via a fused spur, on what looked to be a dedicated circuit, from the non-RCD protected side of a MEM split DB (DB2) in the same room. This DB was fed from an upfront RCD from supply 1(not DB1). It is this RCD that trips.
Brief (Friday@19:00) testing showed the up front RCD to be okay. IR @ 500V gave 999MOhms on L-N and L-E but 12.6 MOhms N-E, this was with the MEM board isolated with the boards main switch.
The fan was brand new but I still stuck a flex and plug on it and it works fine on another circuit, on the same RCD.
I know I've a lot to look at when I return but the low N-E IR, whilst not very, is baffling me. It could be a genuine fault but I wouldn't have thought it low enough to cause an RCD to trip. (?)
I could well be going off the deep end but I'm wondering if this is indicative of someone borrowing a neutral for a circuit fed from another board/supply.
If you made it this far and can make sense of this then we'll done. I've rewritten this so many time but it's still clear as mud.