Initially was obviously a hard fault because mcb would not reset. Unscrewed and checked all light switches for obvious fault (some metal) no visual problem, then found possible issue with disconnected wire in ceiling. Rose. Repaired this and initially mcb stayed in. Connected each light switch and checked light in turn and all was fine. Then tripped again after few minutes. Swapped circuit with another 5a mcb to see it was the mcb but fault transferred to new breaker. Removed some boards from loft to see if appeared to be a trapped squashed wire but nothing obvious. Reset mcb and left a light on to see if it tripped again but did not trip and after about 3 hours turned light off so no lights on in circuit, on after a while mcb tripped again. REset breaker successfully.
Looking for ideas to try to find problem which has only been occurring since yesterday
 
Any lights that get hot? Such as recessed halogen 50W downlights that are cooking the wiring, I've seen plenty of charred cabling, connector blocks and sometimes insulation burnt to cause a short, possibly intermittent. Similarly inside light fittings with tungsten or halogen lamps, overheating especially if fitted with lamps higher than the manufacturer's rating.
 
Is the circuit on an RCD as well? If not, then the tripping MCD might be down to water getting into JB or fitting somewhere - either outside, or under piping/plumbing fittings...

If there was an RCD then I'd expect that to have tripped first with water, but even then it's not guaranteed...

Otherwise the only way other than trial and error will be a case of testing IR between live and earth and narrowing it down to a faulty section....

It may be a fault within a cable, so not visible even if you visually check it all, so testing with the right tester may be the only way to narrow it down further...

The obvious things to check are a cable caught at a switch (sounds like you may have tested this), or rubbing on a metal back box - or perhaps a faulty metal light fitting...
 
Any lights that get hot? Such as recessed halogen 50W downlights that are cooking the wiring, I've seen plenty of charred cabling, connector blocks and sometimes insulation burnt to cause a short, possibly intermittent. Similarly inside light fittings with tungsten or halogen lamps, overheating especially if fitted with lamps higher than the manufacturer's rating.
I do have recessed lights but these are on a different circuit which is not a problem. I have. Chandelier with a metal ceiling cap but this is rarely on and has not been on for some weeks now. I also do not use large wattage lamps anywhere and am puzzled when it trips when no lights are on
 
Is the circuit on an RCD as well? If not, then the tripping MCD might be down to water getting into JB or fitting somewhere - either outside, or under piping/plumbing fittings...

If there was an RCD then I'd expect that to have tripped first with water, but even then it's not guaranteed...

Otherwise the only way other than trial and error will be a case of testing IR between live and earth and narrowing it down to a faulty section....

It may be a fault within a cable, so not visible even if you visually check it all, so testing with the right tester may be the only way to narrow it down further...

The obvious things to check are a cable caught at a switch (sounds like you may have tested this), or rubbing on a metal back box - or perhaps a faulty metal light fitting...
The circuit and mcb is protected by an RCD and that does not trip, that is why I am puzzled as an earth fault would be more likely to have tripped the RCD first. Also puzzled while it has seemed to trip even when there is no load on circuit, after leaving a light on for some time and not tripping, and as of today it has not tripped over night even with metal cased outdoor lights being on a dawn to dusk setting.
 
Is it upstairs with loft ad-hoch boarded over.
( seen wire in conduit , trapped and cut by conduit ends. )
As 7029 Dave says .
..For safety sakes - IR testing is needed ..
 
The circuit and mcb is protected by an RCD and that does not trip, that is why I am puzzled as an earth fault would be more likely to have tripped the RCD first. Also puzzled while it has seemed to trip even when there is no load on circuit, after leaving a light on for some time and not tripping, and as of today it has not tripped over night even with metal cased outdoor lights being on a dawn to dusk setting.Have just checked fuse board again
 
Is it upstairs with loft ad-hoch boarded over.
( seen wire in conduit , trapped and cut by conduit ends. )
As 7029 Dave says .
..For safety sakes - IR testing is needed ..
I live in a bungalow and loft is ad hoc boarded over. As said earlier i lifted some of boards and checked for damaged cabLes but did not notice any. It has not tripped since sunday after I checked around, however I have a normal Fluke multimeter tester with resistance testing. would this be suitable to test the insulation of the live to earth of would it need a specific ‘megger’ type tester, and if so would you suggest removing the main feed from fuse board and testing here to earth be enough and what resistance reading would be acceptable
 
You would need a purpose-made insulation tester. A normal mulitmeter wouldn't tell you much unless there's a dead short (which is unlikely given the lights at least sometime work).
It would be cheaper to have someone spend <1 hour checking it it than to buy an IR tester. This sort of work also requires care and experience to avoid damaging anything while testing.
 
You would need a purpose-made insulation tester. A normal mulitmeter wouldn't tell you much unless there's a dead short (which is unlikely given the lights at least sometime work).
It would be cheaper to have someone spend <1 hour checking it it than to buy an IR tester. This sort of work also requires care and experience to avoid damaging anything while testing.
Yes I guessed it would need a proper insulation tester like a megger tester.
 
Can you tell what gauge wire it's wired in , as I was amased how many amps must have flowed in my MCB to have not caused a fire.
(Fresh new dry wood in close proximity --oops)
Typically 1.00 or 1.5mm.
Yep was my "new" .. Old dusty cobweb filled house !
22 years ago.
(Also any external lighting -attached / modern LEDs left on )
 
? If not, then the tripping MCD might be down to water getting into JB or fitting somewhere - either outside, or under piping/plumbing fittings...
Agree. This intermittent fault has all the hallmarks of a "water fault". They can be a right nuisance. Forensic visual inspection of all circuit accessories is one of your best weapons in this situation
 
One situation more common in poorly maintained rental properties.
Candelabras full of dead cheap incandescent SES (Small edison screw ) Lamps ..where you can see the bum marks in the threads as you unscrew them. Holes burnt thru !
They normally only go bang once , but add some occasional vibration/tall people !
 
One situation more common in poorly maintained rental properties.
Candelabras full of dead cheap incandescent SES (Small edison screw ) Lamps ..where you can see the bum marks in the threads as you unscrew them. Holes burnt thru !
They normally only go bang once , but add some occasional vibration/tall people !
As I have only moved to this house in the last couple of years and all lighting has been checked or changed I don’t think burnt wires or old fitting/switches is an issue here. Luckily have had no more trips for 5 days now since first seen.
 
Luckily have had no more trips for 5 days now since first seen.
Ifs it's a result of rain or a leak, then it will likely return. If its the result of other "foreign matter" like a rodent getting stuck in the wrong place, then the entrails causing the short are either vaporised or dried up and that you should be the end of it. Regardless, you will someday discover the cause.
 

Reply to Intermittent lighting mcb triping in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I'm not sure what's going on with my kitchen light. I've replaced an old 28W CFL fitting with a new 4 x LED GU10 fitting (a cheap one from...
Replies
11
Views
1K
Hi I know I have to do more testing but I just want to see if there is something I’m missing. Customer said light fitting in the loft was...
Replies
11
Views
1K
Hi, looking for some ideas on this. I went to an address on Tuesday following a storm where property has been struck by lightning. When the...
Replies
3
Views
724
Hi all, There's 2 single fan ovens in the house my mother recently moved into. Posh elecronic AEG units. It's been sat empty for a year, so the...
Replies
19
Views
1K
Hi all, Wondering if you could offer some advice please. I carried out a small outdoor lighting project today at a commercial property. 4 lights...
Replies
5
Views
859

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock